Discuss Breakers upside down in the UK Electrical Forum area at ElectriciansForums.net

Bob Geldoff1234

-
Esteemed
Arms
Reaction score
767
Called to a house today to just change some switches and went to the mains to switch off.This is what I was presented with.
IMG_20190313_115306777.jpg

If you notice all the breakers have been put in upside down.

My question is would they still work in a fault condition in that position?
 
Fuses and MCBs don’t care which way round they are.
Single module RCBOs can only be fitted one way.
Double module RCBOs and RCDs will operate if round the wrong way, but the test button may not.
 
Have you opened it? If the breakers are upside down it could be worth checking where the busbar is and make sure its clamped properly. I'm not sure if the top and bottom terminals are in the same position.
 
bloody obvious. the installer was australian. come on guys.it'snot rochet skienke.

Why didn't they put the main switch upside down then. If they wanted to be clever they could of installed 'em the right way up, but just put the labels upside down. Would of been quicker. :)
 

Reply to Breakers upside down in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Need to replace an old Vent-Axia extractor fan as the pull chord no longer works. I bought this -...
Replies
19
Views
1K
I'm not an electrician. I clean cookers and today arrived to a rangemaster range cooker. Got started, and as part of my routine, I turn on ovens...
Replies
1
Views
799
Extremely low voltage on 120v line Hi, I’m not an electrician but my home has 20 amp breaker that has only one outdoor outlet on it with a GFCI...
Replies
2
Views
571
I recently purchased a rural property in Arizona. The property receives power from APS, the local electric utility. Power arrives from the...
Replies
3
Views
891
Hi all. I have a power outlet that has no power coming to it. The breakers all appear to be untripped (I turned them off & on again to make...
Replies
2
Views
772

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock