o.k. bs 1361 fuses have earth fault loop impedance times as follows
80A-0.40ohms
100A-0.29ohms
(yes based on 80% values, 5 secs distribution)

In a TNS you can goto a max 0.8ohms Ze
so even if you use the smallest rated fuse in your service head, 60A still max only 0.56ohms and your Ze was 0.8ohms (TNS) it would not hit the required 5sec time??
 

Reply to bs 1361 fuses service head in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi, first question on here in a very long time, I am hoping for some nice replies ?. It's been playing on my mind all week and can't seem to find...
Replies
12
Views
4K
Hi First time with this kind of a job for me. I have a scenario where i am planning to install about 50m 25mm TPN from a TNCS supply to supply a...
Replies
32
Views
6K
Landlord has had an EICR done on the property as is required under the new PRS legislation, got a copy of the report and I'm not overly impressed...
Replies
15
Views
3K
Hi all, first post, and it relates to quite a challenging installation. The short version is that I'm working through remedial work on a 75 page...
Replies
13
Views
6K
Hi Guys, i came across an old MEB service head the other day when carrying out a landlord check, I've not come across one of these before and...
Replies
6
Views
6K
Octopus
O

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock