Can anyone give me some clarification on the following.

I am installing some Osram Planon Plus led light panels into a temporary building and have been told the transformers need to housed in an enclosure as they do not have the correct markings for BS7671 "max surface temperature under fault condition".

Im a mechanical design engineer and not disagreeing with the request but want to understand the regulation and why these off the shelf units need additional enclosures in order to be used.

Many Thanks in advance.
 
421.1.2 Fixed electrical equipment shall be selected and erected such that its temperature in normal operation will not cause a fire. This shall be achieved by the construction of the equipment or by additional protective measures taken during erection.
The heat generated by electrical equipment shall not cause danger or harmful effects to adjacent fixed material or to material which may foreseeably be in proximity to such equipment.
Where fixed equipment may attain surface temperatures which could cause a fire hazard to adjacent materials, one or more of the following installation methods shall be adopted. The equipment shall:
(i) be mounted on a support which has low thermal conductance or within an enclosure which will withstand, with minimal risk of fire or harmful thermal effect, such temperatures as may be generated, or
(ii) be screened by materials of low thermal conductance which can withstand, with minimal risk of fire or harmful thermal effect, the heat emitted by the electrical equipment, or
(iii) be mounted so as to allow safe dissipation of heat and at a sufficient distance from adjacent material on which such temperatures could have deleterious effects. Any means of support shall be of low thermal conductance.

422.3.2 Measures shall be taken to prevent an enclosure of electrical equipment such as a heater or resistor from exceeding the following temperatures:
(i) 90 °C under normal conditions, and
(ii) 115 °C under fault conditions.
Where materials such as dust or fibres sufficient to cause a fire hazard could accumulate on an enclosure of electrical equipment, adequate measures shall be taken to prevent the enclosure from exceeding the temperatures stated above.
NOTE: Luminaires marked D in compliance with BS EN 60598-2-24 have limited surface temperature.

The symbol referred to in the Note above is a d writhing a triangle pointing down.
 
Last edited by a moderator:
Sorry, the site plays up so much, that it’s easier to edit a post than to try to write a long one.
The logo is a D in a triangle pointing down.

Regs regarding temperature under fault conditions only apply to conductors as far as I am aware.
 
Mounting something that has the possibility of overheating, within an enclosure would seem to be completely the wrong choice, it's going to over heat quicker.

I'd be going for mounting in free air as a first choice, if fact I'd can't believe a company like Osram would manufacture something like this so I'd be contacting them and if it is correct looking for an alternative manufacturer first.
 
Mounting something that has the possibility of overheating, within an enclosure would seem to be completely the wrong choice, it's going to over heat quicker.

I'd be going for mounting in free air as a first choice, if fact I'd can't believe a company like Osram would manufacture something like this so I'd be contacting them and if it is correct looking for an alternative manufacturer first.

Mounting on a large piece of metal would be preferable to free air. It'll act as a heat sink.

However I think it is eluding to, if you install in an enclosure, the component that is going to reach >115 deg C will not be in contact with anything flammable.
 
If the panels have a metal enclosure just sit on top and ensure it is not enveloped by anything. As above I would not personally enclose them as this will restrict heat dissipation and the enclosure will also need to kept away from non flame retardant materials.
 
Ok - I hadn't thought about this before, so I had a quick look out of interest. Looking at your transformer it's missing the inverted triangle symbol with the thermal protection temperature. If you look at the pic below, it's saying 110 C, in line with @spinlondon quote from Regs of less than 115 C. I can't say if it's mandatory to have the symbol, but without it we don't know what it's performance will be under fault conditions. The symbol is referenced in BS7671 Table 55.3 . Scanning a few drivers, some have the symbol and some do not. Another Learning Moment for me :) .

IMG_1365.JPG
 
Ian, why the dumb ratings on the posts above? The replies seem pretty helpful to me.
 
Last edited:
I am still reading your replies but also trying to speak with Osram and get some clarification from them. At present I can not use these, but feel I can mount the Transformer on a aluminium extruded T section away from any combustible material.
 
A lesser known but critical LED light specification is the Ta rating. Ta, or “ambient temperature,” is the reference temperature of the ambient air when the product is tested to deliver the rated performance.

This specification is important in critical or harsh environments. For example, in the absence of specific instructions from the manufacturer, the default testing temperature in a laboratory may be only 25° C.

If the luminaire is to be installed into a harsh environment where the average temperature is 45° C, the 20°C difference will have a significant negative impact on the anticipated life of the product.

Furthermore, the other critical reference is the Tc, which is the hottest point of the luminaire component at the time of testing in the selected ambient temperature.

In the theoretical case above, the Tc point on a driver may be tested at 65°C at a Ta of 25°C.

If the actual installation environment has a Ta of 45°, then it stands to reason that the Tc could escalate well above the reliable operating limit for that device.

In summary, the Ta is an important technical specification that should be carefully explored to ensure the product selected is fit for purpose for the intended installation environment.
 
Ian, why the dumb ratings on the posts above? The replies seem pretty helpful to me.
Ask spin as he’s practically went through all my posts and give a dumb rating because he’s spit his dummy out.
He’s done that before to another member so enough said.
So I started to retaliate but thought better.
Petulant I know.
He’s now ignored so I apologise if I’ve come over a bit of an idiot.
He’s not worth it
 
Ask spin as he’s practically went through all my posts and give a dumb rating because he’s spit his dummy out.
He’s done that before to another member so enough said.
So I started to retaliate but thought better.
Petulant I know.
He’s now ignored so I apologise if I’ve come over a bit of an idiot.
He’s not worth it
You reap what you sow.
 
Thats what I thought, although as mentioned earlier I would like to locate the driver on an aluminium heat sink away from combustible material in free air.
Osram are now looking into the issue for me.
Thanks.
 
My take is - the regulation requires less than 115C during a fault and since the manufacturer does not warrant this, you become responsible for achieving compliance. I would choose a driver that included the symbol, one less thing to worry about :) .
 
Last edited:
The intended use is for the light panels, 10-off to be installed into a temporary building, they can all be controlled from one remote, dimmed and temperature (colour) changed. Finding a compliant driver to do this is really quite difficult.
 

Reply to BS 7671 max surface temperature under fault condition ??? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I know how I was taught to test a RCD, 6 tests in all two no go, two under 300 mS and 2 under 40 mS with no load. But thinking about it not so...
Replies
7
Views
3K
V
Hey guys, i have started to do some inspecting and testing, i am finding it very interesting although the certification part is a little confusing...
Replies
26
Views
4K
E
I think I've Posted this before, but I've just updated it. Some of the sparks where I work still get a little confused of what the different areas...
Replies
58
Views
78K
F
I've been having a sort out on the computer and have found some 2391 past papers with answers, the following are questions 1 - 10 short answer and...
Replies
1
Views
4K
richy8ball
R
S
I will post the answers on here in a few day or if you really want to know PM me and i will send them. Example Questions for 2382-10 1. The...
Replies
1
Views
2K
sxsparky
S

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock