Discuss BS EN 60204 Machinery testing in the Industrial Electricians' Talk area at ElectriciansForums.net

Reaction score
2
Hi all, I am an electrician working for a OEM machinery manufacturer based in Germany, we are the local hub that is now taking over the installation of the machines in the UK, the machines are liquid filling, packing and palletizing.

So on to my question, as I understand it the machines themselves from the main isolator coming into the machine and the associated cabling to motors and external components are covered by BS EN 60204 and not BS 7671 (I am JIB approved electrical with BS 7671 18th edition) If we start to carry out the installation they will need to be tested, to my knowledge this is not currently done, but if I am getting involved then I want to make sure it is all done correctly and above board

If it is covered under BS EN 60204 then we don’t need NIC or ECA accreditation, but do we need to get the Inspection and Testing cert, although this is primarily for BS 7671, are there any guidelines for testing on machinery installations that I need to be aware of.

Any thoughts or advice gratefully received
 
The design and construction of the machine would hopefully have been independently verified to the standard you mention (EN or IEC version - same thing) by an accredited laboratory, such as Intertek or SGS or UL or BSI etc. or if your German machinery manufacturer has the in-house capability, by the QA function in the ISO 9001 German company, and a Declaration of Conformity issued detailing the Directives and standards the machine complies with. (electrical safety, mechanical safety, electromagnetic compatibility, maybe environmental, ROHS etc)

If you are working inside the machine I would expect what you do to be covered by the manufacturers procedures/ installation instructions, and for you to be keeping installation records in line with the manufacturers installation checklist or procedure. I would expect such instructions to include details on incoming supply, protection and cable sizes, and any special requirements. As you say, once you get past the cables feeding the machinery, you are in BS 7671 territory.
There are also Health & Safety regulatory and safety standards, and perhaps food hygiene standards, to consider.

If you are not an employee of the German company, but an employee of "the local hub" and you are not being provided with any of this, I would expect your direct employer to have a process in place to provide and monitor the installation, and be certified to ISO9001 to continue the machines installation history/records. If that is the case, the Quality Manager (or his/her department, or Quality Representative) of whoever is employing you should be on this, and providing documentation and guidance. If the 'local hub' is just being set up now, part of that should be implementing company procedures, including Quality Assurance, that will ultimately define installation processes and keep the necessary records. I would hope this would be supported, or even provided, by the German manufacturer, including access to standards and machine documentation.

If there's no infrastructure supporting you, that's an undesirable situation. Usually reputable machinery manufacturers are keen to have some control over their installations and installers, and I would expect some flow of information/ documentation/ training etc. to be coming from them. Perhaps it is, but not getting to you?
One reason why this is so important is that electrical and mechanical safety standards have become more risk based over the past decade or two, and risk assessments are an integral part of machine design, hopefully extending through to installation. So somewhere there will have been brainstorms, hazard analysis and risk assessments trying to predict what needs to be done, including during installation. I would have expected such activity to have produced instructions, if not checklists, for installation. An effort should be made to obtain anything like this!

Working inside the machine puts you in the front line if anything should go wrong, so you are right to be concerned about it.
If your enquiries don't elicit anything useful, and you are pressed into getting on with the job, I suggest as a minimum you keep a log book detailing what you did and what and how you tested, along with photo's.

I just hope you don't end up being the person asked to write the UK installation instructions!

Edit PS: I am aware that the accredited test houses have access to sets of checklists for the various machinery safety standards, so for the particular parts of EN60204 that apply to your filling and packing machines etc. there are huge checklists for compliance with those standards. A far as I'm aware they are not in the public domain, but finding out who did the machine approvals might lead you to someone with access, in which case you (or preferably they) might be able to cherry pick those for salient points.
 
Last edited:
If it is covered under BS EN 60204 then we don’t need NIC or ECA accreditation,
I would say that "the hub" as a business entity should aim to gain ISO9001 registration from an accredited body (eg BSI) (if not already doing that), which would only be achieved when there are procedures and processes in place to meet all the UK legislative requirements (and you will end up with the necessary records).
 
Don't over think this, as long as the main electrical installation has certification and you are not adding a new circuit, the installation of a free standing machine would be the same as hard wiring any appliance.
 
Don't over think this, as long as the main electrical installation has certification and you are not adding a new circuit, the installation of a free standing machine would be the same as hard wiring any appliance.
Though a bit more complex when being integrated into a production line with flow control and e-stops etc. and with H&S implications both for factory staff and consumers of products (if food or drink).
Not that I know that is exactly the case here !!
 
Don't over think this, as long as the main electrical installation has certification and you are not adding a new circuit, the installation of a free standing machine would be the same as hard wiring any appliance.
Just to clarify, this is not a simple stand alone machine, it is a whole production line, from empty cans coming it, product mixing, cleaning, filling, checking, packing, transport, robot palletizing, to pallet transport, covering an area of 2 football pitches on multiple levels
 
I would say that "the hub" as a business entity should aim to gain ISO9001 registration from an accredited body (eg BSI) (if not already doing that), which would only be achieved when there are procedures and processes in place to meet all the UK legislative requirements (and you will end up with the necessary records).
Yes it is in the Food and Drink industry and I believe we are ISO9001, the Electrical drawings and documentation is to ISO 16016
 
Yes it is in the Food and Drink industry and I believe we are ISO9001, the Electrical drawings and documentation is to ISO 16016
Worth asking for/checking the 'Scope of registration' on the ISO 9001 certificate to see if it covers installation as part of the business offering. If it does, I would hope the periodic (6 month?) surveillance visits would include the auditor(s) wanting to look off site, or at least see installation procedures and records. And I would hope the QA bod and you would be talking!
If not within the scope at the moment, something for the organisation to think about. It ought to help you!
 
Worth asking for/checking the 'Scope of registration' on the ISO 9001 certificate to see if it covers installation as part of the business offering. If it does, I would hope the periodic (6 month?) surveillance visits would include the auditor(s) wanting to look off site, or at least see installation procedures and records. And I would hope the QA bod and you would be talking!
If not within the scope at the moment, something for the organisation to think about. It ought to help you!
I'll look in to this when I am in the office tomorrow
 

Reply to BS EN 60204 Machinery testing in the Industrial Electricians' Talk area at ElectriciansForums.net

Similar Threads

Morning all, We are looking at qualification requirements for inspection and testing to BS EN 60204, all of our work is past the main isolator of...
Replies
2
Views
718
Hi All I’m in charge of the maintenance (machinery and facilities) in a plastics manufacturing business. I have a ‘team’ of little old me and an...
Replies
3
Views
1K
Hi, I'm having a new boiler fitted in a new location. I need to provide power for the boiler which I'm looking to do myself. Boiler: Ideal Logic...
Replies
11
Views
2K
We have started a business building garden rooms/caravans/mobile homes under the caravan act. We have only done one so far and I got an...
Replies
3
Views
1K
I've started to move over to AMD 2 forms for my CU installs, if only because the schedule is so much easier to tick and I can stop sticking labels...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock