Discuss bs no. of main supply fuse (attached pic) in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Reaction score
39
Does anyone know the bs no of the fuse on the attached pic and how do I find out the earthing arrangment without taking the cover off?
 

Attachments

  • 20121113_114857.jpg
    254.1 KB · Views: 100
Hi Dave
Very clever trick that someone on here pointed out;
Measure Ze then measure loop impedance between line and neutral. If they are the same then it's an earthed neutral, if there is a difference then they are seperate.

Hope that helps
Laurie
 
That Terminal block for the earths joins into the neutral. So that makes it PME TNC-S. The fuse is probably a BS1361 or a BS88. No real way of knowing (that I know of) which it is until it is removed and looked at.
I see that the seal has already dropped on the floor......so I would remove it and look......just to make sure.
 

Reply to bs no. of main supply fuse (attached pic) in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

When doing an EIC for an additional circuit (which only covers that circuit), does the 'main switch/switch-fuse/circuit-breaker/RCD' section refer...
Replies
1
Views
1K
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K
Hi everyone, When checking my consumer unit voltages with the full board off, I stumbled across something head scratching. Measuring the feed...
Replies
1
Views
615
Hello fellow electricians, Would anyone know how to connect a Nalder Bros & Thompson LTD London, please? ~The BS 89 is a tough book to obtain. I...
Replies
7
Views
818
Hi, Posted here as I'm not an electrician, not because it relates to anything I'm considering "Doing Myself". My late parent's house is supplied...
Replies
5
Views
174

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock