So every BS 7671 edition I have is only valid for designs after a set date, so you will need the installation certificate to get the design date and a van full of reference books to select the correct year. As when each current edition was current it refers you back to older editions when not a new installation, this was why I did not agree with removal of code 4
 
So every BS 7671 edition I have is only valid for designs after a set date, so you will need the installation certificate to get the design date and a van full of reference books to select the correct year. As when each current edition was current it refers you back to older editions when not a new installation, this was why I did not agree with removal of code 4
Why would I need this if I am conducting the inspection and test to the current edition of BS7671?-

"GN3 3.12 Periodic inspection of installations constructed to an earlier edition of BS7671 or the IEE Wiring Regulations
People often ask what standard should be applied when carrying out the periodic inspection of an installation constructed in accordance with an earlier edition of BS7671, or an even earlier edition of the IEE Wiring Regulations or to an unknown standard. Each edition of the Wiring Regulations has provided for an increase of safety to the users of the installations. Particular installation practices and methods that were compliant with earlier editions would be considered to be unacceptable now, such as the use of a public water pipe as a means of earthing, which would be considered as potentially dangerous now.

In all cases the inspection should be carried out against the current edition of BS7671. (italics mine)

It is likely that there will be items that do not comply with that edition but this does not necessarily mean that the installation is unsafe. If the inspector considers that an item, although not warranting Code C1, C2 requires improvement, it should be given Code C3 on the Electrical Installation Condition Report. If the item does not require improvement it does not need to be recorded as an observation."
 
As said your looking for degrading and danger, not compliance with any edition of BS 7671, in most cases it is the same, but to say anything passes or fails just because it complies or does not comply with BS 7671 is not enough.

The problem as I see it is other regulations and laws, BS 7671 is not law, but there are fire regulations which have caused changes in the BS 7671 which are law, if I make any reference to fire regulations I run the chance of getting it wrong, and I need to make it very clear I am only testing for electrical safety.

I had a home buyers report, which included reference to the electrical installation, where it referred to the condition of the electrics, it as a result is an electrical installation condition report, it reports on the electrical installation condition, but it is clearly not what we would call an EICR.
 

Reply to BS7671 524.1, C2 or C3 in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net

Similar Threads

Good Afternoon All Currently doing an EICR on common parts of a big site with multiple blocks. All blocks have outside garden spike lighting in...
Replies
11
Views
594
I've tried to research and form a plan without asking on here, but I'm just going around in circles. Just completed an EICR. The wiring ranges...
Replies
15
Views
2K
Fun EICR at an HMO today, which was installed new 5 years ago (not particularly well!) Lots of niggly things that I'll sort, but in the kitchen...
Replies
61
Views
5K
Morning all So the site I'm based at recently had some work done (think partitioners). This package of work included electrical. This was...
Replies
47
Views
8K
I have recently had an EICR on my tenanted 1st floor purpose-built flat, built in 1995. I have received C2 codes for lack of RCD as follows: 5.14...
Replies
16
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock