Discuss Bungalow bathroom fan, no external walls in the UK Electrical Forum area at ElectriciansForums.net

timhoward

-
Esteemed
Arms
Supporter
Reaction score
8,907
I've just had a look at an extractor fan not working. As per title it's a bungalow and there are no external walls, so it vents through the loft and roof.
Earlier this year the customer requested a more powerful fan and the sparks fitted a Manrose inline unit. Fair play.

But the thing is, there's a vertical ducting run from the Manrose unit to the roof vent, and when I got there I emptied half a bucket of water from the vertical ducting and the fan.
I happened to see the neighbour who obligingly let me look at their setup, which was the original ceiling mounted fan and some heavily cladded ducting going straight up. I guess any condensation would simply fall down and through in that scenario.

Options as I see it are:
a) change it back to a ceiling fan and try and find some insulated ducting and reinstate a directly vertical run. Customer not keen as the fan location isn't above the bath and they wanted a better solution.
b) fit another Manrose unit, insulated ducting and presumably some kind of condensation trap.
c) Change to a very long horizontal pipe run through the bungalow side wall, this would be at least 6-7m of pipe.

I'm thinking a) as it's apparently worked for years before, but glad to hear any thoughts or previous experiences.
 
Did the Manrose fan have a backdraught shutter or flaps on or in the ductwork?

The ducting in the loft should be insulated anyway but some if not all of the condensation you emptied out will be from when the duct was trying to act as a chimney without the fan to push the warm air out of the roof.
 
No, very primitive and optimistic install…
F2D49D3E-DAC6-4E76-BB67-B5DB601CF2A2.jpeg
7616FCD3-2BE5-4900-A99A-9CD546BF9EC5.jpeg
 
Probably condensation, though on a referb we are doing at the moment a currently unused tile vent in the roof is defective and allows substantial amounts of water in when it rains. They are waiting for the roofers to replace it before the new ceiling is fitted. Worth a thought just in case.
 
Edit, I can't believe the effort they went to to fix the left side of the banding with 3 screws but failed to use insulated ducting in the cold roof space.

I tend to hang larger inline fans off loose large cable ties to stop the motor vibrating the ceiling, keeping the motor closer to the outlet vent than the ceiling also cuts down on noise in the bathroom
 
is there an overhanging eave nearby that's closer than a gable wall?

fan mounted a little higher... suspended as Freddo suggests, with a solid duct downward slop... just a bit of flexy at the end
 
MF100, they're quite powerful fans. You can cover the fan unit itself with insulation to help reduce condensation (I have an email from Manrose confirming this).

I have done C), with a similar length of rigid duct (100mm plastic tube stuff), and it was still powerful, shifted the air nicely. You can lift the loft insulation and lay it over the top of the duct, again to reduce condensation.

Also have done B), again using rigid duct, with loft insulation fixed round the outside with cable ties.

For the same reason as @freddo , I prefer to fix the fan to the rafters (sometimes suspended via timber) rather than the ceiling joists, to prevent vibration. Very short lengths of flexi duct, connecting the in/outlets of the fan to the rigid ducting also prevents the vibrations transfering to the rigid duct.
 
Surely the point of a bathroom extract is to take out the condensation in the room and the fan being powerful enough to move the condensation to another area, the problem as I see it is the corrugated ducting moist ladened air will deposit water droplets onto the corrugations and are then sheltered by them, smooth ducting would prevent this, IMO insulation around the ducting and fan is to reduce noise.
 
@timhoward maybe originally it had a pasivent fitted, which were just a grille with a flap which opened with steam and went straight up in insulated duct, no electric. ive lived somewhere with those before.

If you really cant get to a soffit or out the gable maybe move the fan to be closer to the roof, fixed to truss so its only got a short exhaust, so the inlet side drops away back straight to the grille, at least then it will drip back out the grille and not collect in the motor, insulated duct.

Or theres the inserts you can fit inline that drain away condensation, but youd need somewhere to run it
 
If you use solid ducting, you can use these;


Or has somebody mentioned that..
Some of these are designed for 100mm ducting, some for 110mm soil pipe. However, you often find the 110mm traps being sold as being 4 inch, or 100mm. Very annoying when you come to do the job and it doesn't fit the 100mm duct you bought (often from the same supplier)!

IIRC the condensation traps that toolstation sell are for 100mm ducting.
 
Some of these are designed for 100mm ducting, some for 110mm soil pipe. However, you often find the 110mm traps being sold as being 4 inch, or 100mm. Very annoying when you come to do the job and it doesn't fit the 100mm duct you bought (often from the same supplier)!

IIRC the condensation traps that toolstation sell are for 100mm ducting.
Sorry bad example link, but as you said 100mm are available. Just need to pipe the condensation to somewhere.
 
You could link the condensation trap back to the shower grill to drip into the shower, when the fan is on it should not drip, but will then drain away through the shower tray once the fan is off.
 
I had exactly the same setup to sort out a few months back... customer reported the fan dripping, then not working. The bathroom had no external ventilation or windows. I went for a 'belt and braces' approach... fitted a more powerful in-line fan, with insulated ducting and a condensation trap that ran out to the gutter. Also added 2 x Louvre vents in the door so that the fan could always draw air from somewhere. No callback since.
 
I had exactly the same setup to sort out a few months back... customer reported the fan dripping, then not working. The bathroom had no external ventilation or windows. I went for a 'belt and braces' approach... fitted a more powerful in-line fan, with insulated ducting and a condensation trap that ran out to the gutter. Also added 2 x Louvre vents in the door so that the fan could always draw air from somewhere. No callback since.
Thanks, that's very helpful to know. I certainly don't want to be the 2nd one who messed it up....

So taking the general principles from the answers I'm intending to get the fan much nearer the roof with a condensation trap and a very short length of insulated ducting to connect to the roof vent. I'm hoping to use entirely rigid ducting from the ceiling to the fan.
 
Or connected back to the shower extract point and drip into the shower tray and hence the tray waste?
Funnily enough the first place I looked to drill out for the drain would have been over a neighbours hot tub....!
It's going to go into a gutter.
I'm all for creative ideas but recycling sweaty steam back into the very place it came from isn't quite ticking the box for me.
 
It's the only way to do it if you don't have access to a gutter or soil pipe, bonnet hipped roofs and soil pipe on the other side of the roofs.
 
Or connected back to the shower extract point and drip into the shower tray and hence the tray waste?
Not sure I understand what you're getting at Mike.

In my experience, the trap is usually fitted just above the ceiling grille, to catch all the condensation from the ducting above, and drain it somewhere where it won't be a problem (eg. to outside the property).

Your suggestion is to drain the condensation back through the ceiling grille? What would be the point of the condensation trap?
 
The 150m2 of slate roof that I spent the first 'lockdown' replacing, had suffered multiple leaks for years, with at least a dozen bowls placed around inside the loft to catch the drips. After it had rained, there was varying quantities of water in these bowls, but after a week or so without rain, most of them would be bone dry.
I suspect that if something with a reasonable surface area, such as a washing up bowl, was placed in a reasonably well ventilated loft, so as to catch the drips from a condensate trap, its contents would evaporate faster than it filled.
 
I suspect that if something with a reasonable surface area, such as a washing up bowl, was placed in a reasonably well ventilated loft, so as to catch the drips from a condensate trap, its contents would evaporate faster than it filled.
And if not, you could run an overflow pipe from the washing up bowl to the gutter or similar.
 

Reply to Bungalow bathroom fan, no external walls in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Got an awkward bathroom fan installation in a downstairs flat, concrete ceilings and (some) walls. Bathroom is already fully tiled and...
Replies
1
Views
656
Hi, I'm looking to install a new bathroom extractor fan in my bathroom as I have a windowless bathroom and the current one I have installed in...
Replies
13
Views
772
Need to replace an old Vent-Axia extractor fan as the pull chord no longer works. I bought this -...
Replies
19
Views
1K
Hi, my niece lives in a flat and has a bathroom without a window. There is an extractor fan which packed up and an electrician installed a new one...
Replies
4
Views
808
This isn't very electrical, but never mind! I'm adding an extractor fan to a bathroom in a 4th floor flat. The builder has helpfully cored a hole...
Replies
20
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock