    Hi there, I am looking for some info on the current regs regarding the burying of junction boxes in my garden for outdoor lighting on a retaining wall.

    The junction boxes will be behind the retaining wall. I am using 3 core SWA and ip66 boxes.

    Upon reading some info I have picked up that junction boxes must be accessible at all times with the caveat that maintenance free boxes can be used.

    Can someone clarify if this is the case for underground outdoor setups as well? Will I need to buy MF boxes lest I make my current boxes accessible for testing etc?

    Thanks

    Rodger.
     
  2. Pete999
    Offline

    Pete999 Trusted Advisor

    Top Poster Of Month

    Location:
    Northampton
    Think you have answered your question, I'm not sure it the box has to be maint free, but the internal connections certainly will need to be maint free, perhaps someone else can enlighten both you and me regarding the actual box itself, remember the box needs to be selected properly for whatever environment you are installing it in.
     
  3. Wilko
    Offline

    Wilko Electrician's Arms

    Location:
    Berkshire
    Business Name:
    Wilko Electrics
    The MF standard (BS5733) is pretty tough with lots of testing and so it's expensive for the manufacturers to qualify. A fully compliant set up is for the whole accessory - the box and connectors together. If your JB were compliant, the box would be marked MF, and I'm not aware of anyone doing an IP66 one(?). Best move would be to keep the JB accessible or make a permanent joint as per reg 526.3 .

    I found this IET note helpful :
    http://electrical.theiet.org/wiring-matters/42/junction-boxes.cfm?type=pdf
     
  4. Pete999
    Offline

    Pete999 Trusted Advisor

    Top Poster Of Month

    Location:
    Northampton
    Thanks for that Wilko never to old to learn are we? as an edit, would an metal adaptable box say 4"x4", with Wagos as the connection medium be classed as MF?
     
  5. Risteard
    Offline

    Risteard Electrician's Arms

    Location:
    Derry, Ireland
    Business Name:
    Walsh Electrical Services
    I believe that Wago connectors are only considered MF when used with the appropriate enclosure. (WagoBox?)
     
  6. Wilko
    Offline

    Wilko Electrician's Arms

    Location:
    Berkshire
    Business Name:
    Wilko Electrics
    No worries :)
     
  7. Pete999
    Offline

    Pete999 Trusted Advisor

    Top Poster Of Month

    Location:
    Northampton
    Thanks mate, seems odd though, but I don't make the rules, so in conclusion, for it to be a truly MF joint both box and connectors have to be MF?
     
    • Like Like x 1
  8. Andy78
    Offline

    Andy78 Trusted Advisor

    Location:
    Kingston upon Hull
    I would advise against burying connection boxes unless they are specifically designed for the task. Even an IP66 box filled with water repellent gel can be the culprit of a failed circuit in not too long at all.
    Any cables you bury will need to satisfy the regs regarding buried cables as well. I would consider getting an electrician to design, install and test this project for you.
     
  9. Barry White
    Offline

    Barry White Guest

    If I bury I use resin joints seen too many joints filled with silicone, gell or other gunge all will fail eventually and will be a pain to sort.
     
    • Like Like x 1
  10. Andy78
    Offline

    Andy78 Trusted Advisor

    Location:
    Kingston upon Hull
    Ahuh. Last ones I saw were IP66 boxes with good quality compression glands, all nipped up tight and filled with "magic gel". IR readings were through the floor after 18 months of being installed.
     
    • Like Like x 1
  11. westward10
    Offline

    westward10 In echoed steps I walk across an empty dream. Electrician's Arms

    Location:
    Northamptonshire
    Would definitely use steel boxes, at least that way the armour may get earthed. Keep them accessible with Wagos inside.
     
  12. Rodger Quinn
    Offline

    Rodger Quinn EF Member

    Location:
    KILBIRNIE
    The boxes I have are plastic, using external gland kits and had intended buying the piranha type nuts to carry through the earth for the steel.

    Sounds like resin joints are more reliable anyway so I think I will rethink and use them. I take it I can tee off from a resin joint kit? Any particular recommendation to use?

    I did think about getting an electrician in to do the work but I like doing things myself, learning the proper way to do the job and carrying out the work, it's satisfying. Even if that means I'm rolling about the solem of the house or trawling the internet for answers

    The job will be inspected, tested and certified before burial by a certified electrician so that I can add the certificate to my current building works completion.

    The replies are much appreciated, thanks for the help.
     
  13. Midwest
    Offline

    Midwest Electrician's Arms

    Location:
    Oxfordshire
    You could try the plastic bag IP rated joint box

    IMG_0338.JPG
     
    • Like Like x 1
  14. Midwest
    Offline

    Midwest Electrician's Arms

    Location:
    Oxfordshire
    Sounds like the work is part of building work subject to planning or building regs, or the equivalent in Scotland where I believe you are from OP? The circuit could also be new? I'm not sure where Scotland is with third party inspection & testing, so you might need to tread carefully.
     
  15. westward10
    Offline

    westward10 In echoed steps I walk across an empty dream. Electrician's Arms

    Location:
    Northamptonshire
    Don't want to be using biodegradable bags for that.
     
    • Like Like x 2
  16. sparkdog
    Online

    sparkdog sparkdog Electrician's Arms

    Location:
    Sunny Sussex
    Business Name:
    C MacRae Electrical
    I use Pratley underground boxes.
     
    • Like Like x 2
  17. Rodger Quinn
    Offline

    Rodger Quinn EF Member

    Location:
    KILBIRNIE
    This is a consideration I hadn't foreseen. I will contact the council tomorrow and get confirmation on that, thanks.
     
  18. Murdoch
    Online

    Murdoch Electrician's Arms

    Location:
    Woking
    Like this one I found yesterday when doing some fault finding.... NOT!

    Metal box.jpg
     
    • Like Like x 1
  19. haj
    Offline

    haj Electrician's Arms

    Location:
    Yorkshire
    I believe Wago now do an IP rated box
     
  20. Andy78
    Offline

    Andy78 Trusted Advisor

    Location:
    Kingston upon Hull
    They do the Wagobox capsule, but like all boxes, the IP rating is only offered as the box is sold, and is compromised as soon as you drill and add your own glands. It's up to you to make sure your cable entry method maintains a similar IP rating.
     
    • Like Like x 1
  21. Risteard
    Offline

    Risteard Electrician's Arms

    Location:
    Derry, Ireland
    Business Name:
    Walsh Electrical Services
    Sort of. It's maybe the enclosure rather than the connectors which are certified "MF" - but that certification only applies when used with the specified connectors (in this case Wago connectors in the WagoBox). I suppose it's down to how the unit was when it was granted MF certification. So to use something else inside it would negate that.
     
  22. Risteard
    Offline

    Risteard Electrician's Arms

    Location:
    Derry, Ireland
    Business Name:
    Walsh Electrical Services
    I bet your bank balance doesn't like them though!
     
  23. sparkdog
    Online

    sparkdog sparkdog Electrician's Arms

    Location:
    Sunny Sussex
    Business Name:
    C MacRae Electrical
    Expensive but does a proper job.
     
  24. Rodger Quinn
    Offline

    Rodger Quinn EF Member

    Location:
    KILBIRNIE
    Thanks for the replies, folks.

    I have contacted WAGO direct about their IP rated capsules and connectors to make sure they carry the BS5733 marking and the MF logo. If they confirm, I'll place an order with them.

    I do wonder if an empty box has to have a particular specification to meet MF spec, and what that may be, or whether it's more to do with the type of conductor securing methods utlised inside that deem it's suitability.

    Regards

    Rodger
     
  25. Wilko
    Offline

    Wilko Electrician's Arms

    Location:
    Berkshire
    Business Name:
    Wilko Electrics
    Hi Rodger - the MF logo is seen on the box (if it's an approved one) but for the joint to be 5733 rated as MF, it must have been standards tested and approved as a unit, i.e. connectors and box tested together. So a Wago MF marked box does not make a MF accessory when used with Wago 221 connector for example, as this connector is not yet certified as MF, afaik.
     
    Last edited: Dec 12, 2016
  26. Rodger Quinn
    Offline

    Rodger Quinn EF Member

    Location:
    KILBIRNIE
    So technically even the wago capsule can't be rated as MF since it isn't supplied with connectors.
     
  27. Rodger Quinn
    Offline

    Rodger Quinn EF Member

    Location:
    KILBIRNIE
    Reply from wago

    Hi Rodger, The Wagobox-Capsule is an adaptable enclosure so you need to cut holes to fit glands to suit the cable you want to use. Consequently BS 5733 MF isn't an applicable standard for this type of enclosure. Bear in mind that the Wagobox-Capsule is designed to be maintainable solution for applications like garden lighting. It can be shallow buried with the appropriate glands but is not intended for deep buried permanent joint applications where you would more typically use a resin filled joint. Hope this feedback is helpful. Please don't hesitate to give us a call if you would like to discuss this further. 01353 666011.
     
  28. Wilko
    Offline

    Wilko Electrician's Arms

    Location:
    Berkshire
    Business Name:
    Wilko Electrics
  29. Rodger Quinn
    Offline

    Rodger Quinn EF Member

    Location:
    KILBIRNIE
    Yeah, I've pretty much resigned myself to using resin joints. Of course, I need the T or Y branch sort which seem to have attached quite the price increase compared to the straight through type. Just my luck.
     
  30. jackhammerJIM
    Offline

    jackhammerJIM Regular EF Member

    Location:
    north yorks
    If you are Teeing off in flex use a through joint . Drill a small hole in the top of the jointing kit for the flex . The resin will seal the hole .
     
  31. Rodger Quinn
    Offline

    Rodger Quinn EF Member

    Location:
    KILBIRNIE
    I've already ordered the branch kits :(
     
  32. soms
    Offline

    soms Trainee Access

    Location:
    Somerset
    Not sure about the Prysmian ones but have witnessed two 'Y' resin joints from the wholesaler which were a complete mare, cheap flimsy case with no cable retention whilst performing terminations, so little space to get stuff arranged and such awkward terminations. Then you tape the ends up to hold the resin whilst it sets. Unbelievable really.
     
  33. Rodger Quinn
    Offline

    Rodger Quinn EF Member

    Location:
    KILBIRNIE
    Even the 3M, assuming good quality, ones I saw on Youtube had the ends taped with self amalgamating tape to seal the ends.
     
  34. Wilko
    Offline

    Wilko Electrician's Arms

    Location:
    Berkshire
    Business Name:
    Wilko Electrics
    I think you have correctly described them :eek:
     
  35. Andy_G
    Offline

    Andy_G EF Member

    Location:
    Derby
    Business Name:
    Sparkatron
    I
    think if the joints are maintenance free but the enclosure wasn't,then that would soon render the 'maintenance free' joints as in need of maintenance, therefore all parts of the system will need to be maintenance free. A chain is as strong as its weakest link is the best analogy I can think of
     
  36. telectrix
    Offline

    telectrix Scouser and Proud of It Trusted Advisor

    Location:
    cheshire/staffordshire
    Business Name:
    Telectrix
Loading...
Similar Threads - Buried junction boxes Forum Date
data cable buried direct in concrete Electrical Forum Sep 6, 2017
Joining a cable to be buried in a wall Electrical Forum Aug 2, 2017

Share This Page

Users found this page by searching for:

  1. how much cm is the standard of junction box buried in to wall

  • Electricians Directory Post a Domestic Job Post a Commercial Job