Discuss Burned wires on resistance faston connection on professional Coffe machine in the UK Electrical Forum area at ElectriciansForums.net

light767

DIY
Reaction score
0
Hi all

I have a professional coffe machine working at 220 V and it currently drain about 2,5 kW of power. I have made this simple and horrible schematic here just to explain how it works:
Circuito.jpg

Some time ago I changed the fastons on the resistance from brass faston to stainless steel faston and some time after, this is what happen:

Immagine WhatsApp 2023-10-17 ore 21.25.09_feee052f.jpg


As you can see the wire on the bottom is completely burned and as I did not notice that immediately also the general switch and the safety thermostast get damage. So I changed the general switch, the safety thermostat and cutted the burned wire so I put everything back toghether.
I did a full restoration of the machine but I did not change the eletrical wires because they looked good ( they are industrial ones and have a 2.5 mm^2 section ) even if they hare 20 years old now.
Now this happen again on the other side:


Immagine WhatsApp 2024-02-02 ore 14.03.44_460c08c6.jpg


I'm wondering if this can be related to the stainless steel material of the faston that maybe can produce and overheating due to the fact that the electrical condutivity of the stainless steel it's worst then the one of the brass faston. This never happen with brass faston. So what do you think?
 

Attachments

  • Circuito.jpg
    38.9 KB · Views: 4
  • Immagine WhatsApp 2024-02-02 ore 14.03.44_460c08c6.jpg
    332.4 KB · Views: 4
Hi all

I have a professional coffe machine working at 220 V and it currently drain about 2,5 kW of power. I have made this simple and horrible schematic here just to explain how it works:
View attachment 113059
Some time ago I changed the fastons on the resistance from brass faston to stainless steel faston and some time after, this is what happen:

View attachment 113060

As you can see the wire on the bottom is completely burned and as I did not notice that immediately also the general switch and the safety thermostast get damage. So I changed the general switch, the safety thermostat and cutted the burned wire so I put everything back toghether.
I did a full restoration of the machine but I did not change the eletrical wires because they looked good ( they are industrial ones and have a 2.5 mm^2 section ) even if they hare 20 years old now.
Now this happen again on the other side:


View attachment 113062

I'm wondering if this can be related to the stainless steel material of the faston that maybe can produce and overheating due to the fact that the electrical condutivity of the stainless steel it's worst then the one of the brass faston. This never happen with brass faston. So what do you think?
It will be caused by the terminations not being secure, it may be that the SS ones you have fitted are not as good fit on the terminals as the originals.
 
Some fast-on terminals have a higher current rating than others, you need to see the datasheet for the particular brand you're using; I've seen 6.3mm female fast-on terminals with a 5Amp rating as well as 10 Amp and I'm guessing this is because they're made of thinner material. Also avoid cheap Chinese items from ebay and amazon like the plague and wherever possible use a crimping tool that's the same manufacturer as the terminals. We always use Hellermann Tyton or BM crimps and crimping tools and have never had problems.
 
A crimping tool that is designed for copper terminals, may well not put enough pressure on the terminal to hold the cable correctly if used with stainless steel terminals as they are considerably harder to deform.
 

Reply to Burned wires on resistance faston connection on professional Coffe machine in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello, I am a Trainee here on the Forum. I am seeking some further advice/input on a specific technical matter of importance to me. Briefly, I...
Replies
12
Views
2K
Hello Electricians I'm after some general but professional advice, figured this forum would be a good place to ask and would really appreciate...
Replies
29
Views
12K
Toneyz
T

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock