Discuss Burnt Main Downstream Neutral in the UK Electrical Forum area at ElectriciansForums.net

E

ennaress

Did an EICR opened the CU and found this burnt charred Neutral running downstream of the (main switch). What should I be looking for (other than a replacement tail)?
There were two or three C2 observations that may well have caused an overload - eg 5kW of water immersion wired into the ring final and the oven run off a 13a plug, but the live conductors looked OK.
Installation over 35 years old.
OC or very low IRs on all circuits.
R1+R2 ok as was Zs.
I know one answer would be a whole re-wire, but I want to know what caused this.
Thanks for any helpful replies

20170720_114228.jpg
 
That CU looks a right mess, I would be looking at the integrity of all connections paying particular attention to the N busbar, what a mess that is.
5KW on a RFC are you sure?
I foresee a CU change on the horizon. As well as some redirection of the RFC if that 5KW is correct, oh my.
 
The neutral connection is the sheaving degrading or it is the flash from the camera?

Nice amount of copper from the neutrals on show and the looped back live on the B6 breaker.
 
From the pattern of heat distribution the neutral busbar terminal connection was loose or contaminated and the heat generated as the installation current passed through the resistance exacerbated the damage and increased the resistance and the heat and so on.
That connection should be good for over 100A so overload is an unlikely cause.
 
The neutral connection is the sheaving degrading or it is the flash from the camera?

Nice amount of copper from the neutrals on show and the looped back live on the B6 breaker.
Sheaving???
 
Has the insulation at the top of Neutral gone dry/brittle ,
can see where it's "flowed to blobs" .
RCD end doesn't look as tarnished !
(Nip it up - not completed?)
(or later diagnosis/messing about-RCD-tripping)
 
Where was the combustion on the plastic cu?
Loose neutrals and all that
Plastic will often lump together due to its molecular make up when exposed to heat. The heat here was insufficient to cause thermal breakdown of the molecules and hence no gas is released which would be required to create ignition.
 
Plastic will often lump together due to its molecular make up when exposed to heat. The heat here was insufficient to cause thermal breakdown of the molecules and hence no gas is released which would be required to create ignition.
What answer was a proper physics teachers response.
Thank you sir. :D
 
To cover you behind send the customer a Danger Notice without delay. It looks too far gone to be cured by tightening the screw up. What do you mean by IR is open circuit (OC) ?, if it is how have you got satisfactory r1+r2 ? You have what is known as "guilty knowledge" of a potential fire risk. Ideally tell them it must be isolated and the C.U. replaced immediately, I realise that may not be practical, so send the Danger Notice and make it their problem not yours ! Sorry if I sound like an arse but where there's a blame, there's a claim !! .
 

Reply to Burnt Main Downstream Neutral in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
I have been asked to look at this report as the customer has been given (in their words) 'A very high quote plus VAT'. It doesn't look well...
Replies
5
Views
635
This from a while ago but reading about everyone elses problems tonight made me remember this one. The original job was the lights in a recent...
Replies
1
Views
1K
I'm having an extension built and the builder leading the project has said that the electrician will be over in about 4-6 weeks to start his works...
Replies
4
Views
2K
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock