Hi, I've recently put in a completely new wiring system into my house.

All the circuits are working as they should but the 2no. light circuits in the kitchen are making a buzzing sound.

The downlights are the Ansell Prism colour selectable LEDs. I have these across the entire house and the rest work just fine.

I have checked all the downlights for any loose connections and all seem to be as they should be. I have also removed all but the first downlight from each circuit and the light fitting is still buzzing.

I know this is common when dimmers are concerned but this is a standard light switch (BG Nexus type).

Has anyone come across this or have any ideas on what may be the problem?

Thanks, Dean.
 
Assume you've carried out your intial testing & inspection of this circuit? Have you tried connecting the 'buzzing' luminaires to a 'bench circuit' from say a socket outlet?
 
The project is still on-going. I simply connected them into the CU yesterday to enable works to carry on with lights in the evening.

I'll carry out the tests on the circuit and try the first spotlight on a socket outlet as suggested also.

Thanks Midwest.
 
The project is still on-going. I simply connected them into the CU yesterday to enable works to carry on with lights in the evening.

I'll carry out the tests on the circuit and try the first spotlight on a socket outlet as suggested also.

Thanks Midwest.

If its a new circuit or altered, it should be tested before energising :)
 
All sorted. I had the spotlights hanging from the ceiling. Due to the amount of lights hanging and on top of that these particular lights being quite loud, the sound in the room was very loud. I checked another light fitting in another room that was fitted into the ceiling and it sounded the same on its own.

They’re all in now making a bit of noise above the ceiling rather than below it at least.
 

Reply to Buzzing sound coming from LED downlights in the Lighting Forum area at ElectriciansForums.net

Similar Threads

  • Article
Electrical2Go - Mega Downlight Deal - Don't miss out! Taking place from August 18th to 20th, we're offering an incredible promotion for...
Replies
1
Views
617
I have purchased spotlights as below, but they are flickering when I dimmed them down to around 15-20%. We have installed 8 x ALUSSO LED Recessed...
Replies
4
Views
1K
Hi :) I'm currently renovating my outbuilding. My electrician has fitted 10 conduit LEDs (that support both leading and trailing edge) and x4...
Replies
0
Views
203
Hi I wanted some advice regarding which downlights company is better from ancell or forum? I have builders doing works in my house but I wanted...
Replies
2
Views
579
Hi all, a very long time I did a swanky grand designs type new build in the middle of nowhere, so in the middle of nowhere that it's a house with...
Replies
1
Views
295

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock