Discuss C2 or C3 ? Wrong brand of mcb in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

newfutile

-
Esteemed
Arms
Supporter
Reaction score
388
Which code would you give to a Wylex board populated with Hagar mcbs ,Wylex main switch and Wylex rcd.
Wylex once told me that nsb and nh breakers are not allowed on the same busbar !
 

Attachments

  • 477B1AC9-FDC1-4C45-84E5-6DDCC5C366E2.jpeg
    225.4 KB · Views: 31
As above, agrees with the BPG #4

Code C3 - Improvement recommended

Mixed branded switchgear components within a consumer unit or distribution board where:

  • there are no signs of thermal damage to component or associated connections
  • the enclosure/assembly hasn’t been modified to allow installation of the component
  • the component is securely fitted and all connections are adequate
  • correct manual operation of the component
  • direction of use of toggles/switches is the same as existing devices
Note: If any of the above criteria is not met, this would warrant a code C2 classification to be recorded.
 
Actually I would like to know why it ended up like that. After all, Wylex MCBs are not exactly hard to come by and Hager are, while good products, not exactly the cheapest choice either.

Very odd!
 
Maybe it had NSB Wylex once, i work for a housing association so its hard to figure out what the contractors thought ,the case was quite badly butchered and cracked so I have installed a new consumer unit today !
 

Reply to C2 or C3 ? Wrong brand of mcb in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

I may well need to change all the MCB's for RCBO's in this board (see picture). Do Wylex RCBO's fit in this board? It is currently fitted with...
Replies
22
Views
8K
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
902
Fun EICR at an HMO today, which was installed new 5 years ago (not particularly well!) Lots of niggly things that I'll sort, but in the kitchen...
Replies
61
Views
5K
Good evening, I have recently moved into a new home and I am having problems with the MCB/RCD tripping (Mem M6 Type 3 - 30mA). It intermittently...
Replies
8
Views
1K
Hello, DIY'er here looking for some advice. In March 2023 we should be getting 5.5kW of solar PV going on the roof feeding into the current...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock