Discuss cable behind 50mm insulated plasterboard in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Where does it say that an RCD or RCBO requires an additional RCD in series as a backup?

In short, it doesn't, and I don't think anyone here is saying that it does, but given the number of faulty RCDs I've come across, in my opinion, you'd be an idiot not to fit an s-type up front as back up on a TT system where the only means of providing fault protection is by way of an RCD.
 
In short, it doesn't, and I don't think anyone here is saying that it does, but given the number of faulty RCDs I've come across, in my opinion, you'd be an idiot not to fit an s-type up front as back up on a TT system where the only means of providing fault protection is by way of an RCD.

I don't disagree that it's a 'good idea' to provide a backup device in the event of a faulty RCD or RCBO where these are the only means of earth fault protection.

I was just trying to get to the bottom of the assertion 'you can't use SP RCBOs on a TT supply'. So is it just the lack of discrimination with the backup RCD in the event of a neutral to earth fault or is there something more fundamental about a TT system that makes SP RCBOs unsuitable (assuming that the particular manufacturer doesn't advise against their use)?
 
Easiest way to look at it is page 45 OSG (green) 5.1.1 (ii)
All live conductors in a TT system and line conductors in a TN, remembering what your neutral is classed as!
 
Easiest way to look at it is page 45 OSG (green) 5.1.1 (ii)
All live conductors in a TT system and line conductors in a TN, remembering what your neutral is classed as!

The regulation that refers to is applicable to the entire installation. It isn't talking about individual circuits.

More often than not, the only effect this regulation has is forbidding the use of three pole main switches for TP TT systems.
 

Reply to cable behind 50mm insulated plasterboard in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

I'm currently refurbishing a room and in the process adding some internal wall insulation. The wall has been stripped and my electrician has...
Replies
5
Views
2K
Hi I've inherited a very tight space, a KMF switch and some split-con for a sub-main to try and tidy up. It's a joyous non-restrained single...
Replies
3
Views
226
Hi all, looking for some clarification on MCB and cable sizes I need to run for a new kitchen. Cables will run through a combination of...
Replies
0
Views
3K
Hi all, Have a relatively simple question. Doing a rewire to make a circuit in a single room. My father is a retired spark, so no worries about a...
Replies
7
Views
2K
We have a room in the house that was the kitchen. That has been relocated to a different area, so the old kitchen has been sold off and the room...
Replies
2
Views
675

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock