Need help check that my cable calculations are correct as still new to doing them.
6A Lighting Circuit 60898 MCB Type B wiring in 1MM²/1MM² T+E supplying a single 10W outdoor light
Length = 3.3M
Zs@db = 0.22
R1 + R2 mΩ/M = 36.20 mΩ/M - Table lt P218 OSG
Correction Factor - 1.2 - Table L3 P220 OSG
R1 + R2 = 3.3 x 36.20 x 1.2 / 1000 = 0.14Ω
Zs = 0.22 + 014 = 0.36Ω
Fault Current = 230 / 0.36 = 638A
Disconnection Time = 0.1s
K = 115
√ I²t / k = √ (638² x 0.1) / 115 = 1.75 Minimum CPC size.
Seems like I will have to make the circuit longer to increase the Zs value which seems ridiculous or change my cable for a larger CPC which also seem ridiculous for a single 10W light.
Can someone check I am doing my calcs right before I go down the rabbit hole of adapting!
Many thanks
6A Lighting Circuit 60898 MCB Type B wiring in 1MM²/1MM² T+E supplying a single 10W outdoor light
Length = 3.3M
Zs@db = 0.22
R1 + R2 mΩ/M = 36.20 mΩ/M - Table lt P218 OSG
Correction Factor - 1.2 - Table L3 P220 OSG
R1 + R2 = 3.3 x 36.20 x 1.2 / 1000 = 0.14Ω
Zs = 0.22 + 014 = 0.36Ω
Fault Current = 230 / 0.36 = 638A
Disconnection Time = 0.1s
K = 115
√ I²t / k = √ (638² x 0.1) / 115 = 1.75 Minimum CPC size.
Seems like I will have to make the circuit longer to increase the Zs value which seems ridiculous or change my cable for a larger CPC which also seem ridiculous for a single 10W light.
Can someone check I am doing my calcs right before I go down the rabbit hole of adapting!
Many thanks