Need help check that my cable calculations are correct as still new to doing them.

6A Lighting Circuit 60898 MCB Type B wiring in 1MM²/1MM² T+E supplying a single 10W outdoor light

Length = 3.3M

Zs@db = 0.22

R1 + R2 mΩ/M = 36.20 mΩ/M - Table lt P218 OSG

Correction Factor - 1.2 - Table L3 P220 OSG

R1 + R2 = 3.3 x 36.20 x 1.2 / 1000 = 0.14Ω

Zs = 0.22 + 014 = 0.36Ω

Fault Current = 230 / 0.36 = 638A

Disconnection Time = 0.1s

K = 115

√ I²t / k = √ (638² x 0.1) / 115 = 1.75 Minimum CPC size.

Seems like I will have to make the circuit longer to increase the Zs value which seems ridiculous or change my cable for a larger CPC which also seem ridiculous for a single 10W light.

Can someone check I am doing my calcs right before I go down the rabbit hole of adapting!

Many thanks
 
Need help check that my cable calculations are correct as still new to doing them.

6A Lighting Circuit 60898 MCB Type B wiring in 1MM²/1MM² T+E supplying a single 10W outdoor light

Length = 3.3M

Zs@db = 0.22

R1 + R2 mΩ/M = 36.20 mΩ/M - Table lt P218 OSG

Correction Factor - 1.2 - Table L3 P220 OSG

R1 + R2 = 3.3 x 36.20 x 1.2 / 1000 = 0.14Ω

Zs = 0.22 + 014 = 0.36Ω

Fault Current = 230 / 0.36 = 638A

Disconnection Time = 0.1s

K = 115

√ I²t / k = √ (638² x 0.1) / 115 = 1.75 Minimum CPC size.

Seems like I will have to make the circuit longer to increase the Zs value which seems ridiculous or change my cable for a larger CPC which also seem ridiculous for a single 10W light.

Can someone check I am doing my calcs right before I go down the rabbit hole of adapting!

Many thanks
Adiabatic's quite tricky to get the head around. You're on the right lines, but as you can see, you've come up with a larger CPC than expected. What is the circuit protective device?
 
Your calculations are correct and as accurate as you can achieve right now (see the note that @Pretty Mouth refers to in order to understand why)

A general comment, remember 543.1.1 - you can either calculate OR select.
In general for smaller size line conductors and shorter lengths it's better to select from table 54.7 which would give you a much more welcome answer!
In general for larger line conductors or longer cable lengths, it's better to calculate.
 
It's hard to get a realistic CSA using the data from BS7671. As you've seen the time only goes down to 0.1s, but real world a fault current like that would disconnect much quicker, giving much lower let through energy (I²t), therefore a smaller CSA.

We're concerned with the worst-case situation: for a B or C type breaker, that will be right at the start of the circuit, where the fault current is greatest. If the conductor can withstand a fault here, it can withstand it anywhere downstream.
 
Let's assume you went for a Wylex B6 .
Here's some data from Wylex:
1673647547709.png



You had 638A prospective fault current and a 6 amp breaker, so the multiple is x 106
That graph shows you that the disconnection time will be less than 0.01 seconds.

If you run you calculation again with 0.01 as the disconnection time you end up with a CPC of 0.55 sq mm!
You obviously need to round this up to something that actually exists, and then be mindful that it it's separate to the cable or buried there are minimum sizes that apply.
You are using T&E so that last bit isn't relevant.
 

Reply to Cable Calculation Help - Adiabatic Equation in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi was wondering if im doing this right. The question in: Determine for a chosen circuit "the minimum possible csa of cpc which will satisfy the...
Replies
26
Views
4K
Hi Help please with the adiabatic I am doing a small design for my course and I can't figure it out. Any advice will be appreciated. Ring Final...
Replies
15
Views
2K
Firstly, please go easy as I'm still a trainee! Working on my L3 2365 I'm having trouble understanding the rationale behind adiabatics...
Replies
3
Views
827
Hi, and thank you to anyone who's taking the time to read my question. i'm struggling with the outcome of an adiabatic equation i'm doing and...
Replies
4
Views
3K
Hi All, I think I have confused myself somehow and feel I am spiraling into further confusion. When I am doing the equation, it is saying the...
Replies
12
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top