Hi All,

I have been searching the forum but can't find this anywhere. Can you please see if my interpretation of this is correct:

50x50 trunking, 2m run with 1 90[SUP]o[/SUP] bend.
4 x 50mm conductors,
1 x 35mm conductor.

As there are no factors for over 25mm[SUP]2[/SUP] I have to work it out manually

50x50 = 2500mm[SUP]2[/SUP] (total space)
-
4x50 = 200mm[SUP]2[/SUP]
1x35 = 35mm[SUP]2[/SUP]
Total 235mm[SUP]2[/SUP] which is less than 45% of the trunking capacity, therefore 50x50 is compliant?

Thanks for your help,
(this is my first post :))
 
Hi Chris
I am using IET On Site Guide green book for reference and as you already know Table E5 goes up to cable size 25 mm sq. and Table E6 is for the trunking sizes. However the rest of the page under table E6 states what to do for cable sizes not tabulated in TableE5 (too long to type out here). It seems you are calculating correctly provided you are using the internal csa of the trunking, and keeping to 45% space factor, and assuming you are not breaking any rules for minimum internal bend radius ( Table D5) And as this is your first post, this is my first reply. Have fun
John
 
two things spring to mind, one is insulation, and the other is how to get them around the 90 degree bend. Some cables are better than others for this and some go to 90C which can help if you are having some issues with load.
 
i take it the op is for some design project or something?
cos in real life the 50mm tails will be hanging out of the 90 degree bend by some distance.
 
Hi All,

I have been searching the forum but can't find this anywhere. Can you please see if my interpretation of this is correct:

50x50 trunking, 2m run with 1 90[SUP]o[/SUP] bend.
4 x 50mm conductors,
1 x 35mm conductor.

As there are no factors for over 25mm[SUP]2[/SUP] I have to work it out manually

50x50 = 2500mm[SUP]2[/SUP] (total space)
-
4x50 = 200mm[SUP]2[/SUP]
1x35 = 35mm[SUP]2[/SUP]
Total 235mm[SUP]2[/SUP] which is less than 45% of the trunking capacity, therefore 50x50 is compliant?

Thanks for your help,
(this is my first post :))

From my Trunking and Cable Data:

Trunking Factor for 50 x 50 One Bend = 1037
Cable Factor for 35mm[SUP]2[/SUP] = 95
Cable Factor for 50mm[SUP]2[/SUP] = 132.7

(4 x 50mm[SUP]2[/SUP]) + (35mm[SUP]2[/SUP])= a Combined Cable Factor of 548.8 + 95 = 643.8 which is less than the Trunking Capacity of 1037 and so complies.
 
Last edited by a moderator:
Thanks all for your replies.

Yeah it's for a design project but I hadn't taken into consideration whether the conductors would fit in the bend. My naivety of the physical size of the cable assumed it would.
MarkieSparkie I would too be interested to find out the source of your cable factors please?
 

Reply to Cable factors in trunking, conductors over 25mm^2. in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi All, I have a client who is developing a plot of land for a single house. Currently, their 100 amp service cut-out is in a cubicle fed by...
Replies
7
Views
1K
B
What is the maximum cable capacity (factor) for 200 x 200 steel trunking 2metres up the wall with a 90 degree bend three metres along the wall...
Replies
5
Views
5K
S
Hi all - can someone confirm my thoughts please Here is the situation: 6 floor hotel 45 bedrooms over 4 floors bottom 2 floors are reception...
Replies
22
Views
2K
R
Hi all, I got given a past exam paper from the 2391 course tutor however it doesnt come with any answers so I thought id put the question and my...
Replies
34
Views
20K
Flakey
F
M
Hi all, very sorry to bother you with triv. I am in the process of sorting out some pretty shocking electics in a house that has been bodged at...
Replies
0
Views
3K
mbga9pgf
M

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock