- Reaction score
- 0
Hi All,
I have been searching the forum but can't find this anywhere. Can you please see if my interpretation of this is correct:
50x50 trunking, 2m run with 1 90[SUP]o[/SUP] bend.
4 x 50mm conductors,
1 x 35mm conductor.
As there are no factors for over 25mm[SUP]2[/SUP] I have to work it out manually
50x50 = 2500mm[SUP]2[/SUP] (total space)
-
4x50 = 200mm[SUP]2[/SUP]
1x35 = 35mm[SUP]2[/SUP]
Total 235mm[SUP]2[/SUP] which is less than 45% of the trunking capacity, therefore 50x50 is compliant?
Thanks for your help,
(this is my first post )
I have been searching the forum but can't find this anywhere. Can you please see if my interpretation of this is correct:
50x50 trunking, 2m run with 1 90[SUP]o[/SUP] bend.
4 x 50mm conductors,
1 x 35mm conductor.
As there are no factors for over 25mm[SUP]2[/SUP] I have to work it out manually
50x50 = 2500mm[SUP]2[/SUP] (total space)
-
4x50 = 200mm[SUP]2[/SUP]
1x35 = 35mm[SUP]2[/SUP]
Total 235mm[SUP]2[/SUP] which is less than 45% of the trunking capacity, therefore 50x50 is compliant?
Thanks for your help,
(this is my first post )