Discuss Cable for cooker andseparate hob? in the UK Electrical Forum area at ElectriciansForums.net

Chris

-
Reaction score
26
Hi all,

When wiring a kitchen and the customer is buying a separate cooker and hob, which combined has too high a load for a single 6mm,
Do you wire two separate circuits with a 6mm for each or one larger cable and have both on same circuit?
 
I tend to get the specifications from the client and decide. I've done two kitchens this year and one had 3 new circuits (10mm for hob and 2 x 2.5mm, one each for fitted oven and microwave) whilst the other had one (10mm for range cooker).

And as @dinger809 says... local isolation for each.
 
I tend to get the specifications from the client and decide. I've done two kitchens this year and one had 3 new circuits (10mm for hob and 2 x 2.5mm, one each for fitted oven and microwave) whilst the other had one (10mm for range cooker).

And as @dinger809 says... local isolation for each.
and a fat wallet to pay for the electrickery.
 
Hi all,

When wiring a kitchen and the customer is buying a separate cooker and hob, which combined has too high a load for a single 6mm,
Do you wire two separate circuits with a 6mm for each or one larger cable and have both on same circuit?

Redo you calculations and don't forget diversity. It is very likely the cooker and hob can both go on a single 4mm cable on a 32 amp MCB.
 
Hi - do you know what are the make / model of the hob and cooker?

Hi,

It was more of a general question as i usually wire in two 6mm with local isolation for both but wondered if there was an easier way where I dont have to install two separate cooker isolators
 
Yes. There is no requirement for isolators at all.

But assuming the customer requires it there is no reason why one isolator cannot switch both appliances. After all if the cooker and hob were not separate you would only use one isolator. You can get dual outlet cooker connection units too. You would also only need one cable and it would most probably be OK with a 4mm cable on a 32 amp MCB.
 
@Chris , you should also take into account manufacturers instructions (nearly all the oven type appliances I've connected up have specified ratings for the OCPD they are connected to) and consider the general guidance in the regs about splitting the installation to minimise inconvenience in the event of a fault (as an example, the first kitchen I did this year suffered a failure of one appliance which resulted in the RCBO supplying it tripping - it wasn't an urgent issue as the hob and second oven had their own supply so the home owner was able to cook).
 
Trouble is manufacturers instructions can be wrong as in this example here. This was with a B & Q oven.

IMG_0165.jpg
 
Trouble is manufacturers instructions can be wrong as in this example here. This was with a B & Q oven.

View attachment 48121

So in that case I would use what I like to call 'common sense' and install a 20A DP isolator near the device (so as to comply with the double pole isolation requirements) and supply it from a 16A MCB/RCBO so as to comply with the 16A fusing requirements.

In the event of something going wrong, you have then complied with the manufacturers requirements of double pole isolation and fusing. Thus your backside is covered.
 
Yes. There is no requirement for isolators at all.

But assuming the customer requires it there is no reason why one isolator cannot switch both appliances. After all if the cooker and hob were not separate you would only use one isolator. You can get dual outlet cooker connection units too. You would also only need one cable and it would most probably be OK with a 4mm cable on a 32 amp MCB.
You're welcome to try and Isolate mine Mate. 4mm 2 is no good need something heavier, 70mm 4 core would just about manage it, providing you get a decent swing at it.
 
You're welcome to try and Isolate mine Mate. 4mm 2 is no good need something heavier, 70mm 4 core would just about manage it, providing you get a decent swing at it.
you been on the bottle pete?
 
Here's mine;

“I said to the gym instructor: ‘Can you teach me to do the splits?’ He said: ‘How flexible are you?’ I said: ‘I can’t make Tuesdays’.”
 
Here's mine;

“I said to the gym instructor: ‘Can you teach me to do the splits?’ He said: ‘How flexible are you?’ I said: ‘I can’t make Tuesdays’.”
Tuesday are not good for me, sorry RSVP
 

Reply to Cable for cooker andseparate hob? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

The electrician that installed my cooker circuit put in 10mm cable with a 32a fuse, a 45a cooker switch and 10mm cable to the backplate for behind...
Replies
23
Views
938
Hi All, We have an old Country villa in Spain. The housing electrics were not good so the house recently has been completely re-wired to a good...
Replies
2
Views
791
I have had my kitchen rewired and plastered. I have had a 6mm t+e on a dedicated 32a circuit for a 60cm electric cooker. In hindsight, had i known...
Replies
11
Views
608
I have just had my kitchen redone and the kitchen rewired with a new 6mm cable installed for an electric cooker. However I have changed my mind...
Replies
10
Views
2K
Hi, searched the forum but cant locate anything similar so apologies if ive missed something. Ive got a new hob to install in the kitchen...
Replies
5
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock