Hi, neighbour has asked if I would run new cable from existing cooker control unit to new oven/grill. The easiest way to run cable without disruption would be under existing kitchen cupboards. Cable would be 2.5mm or 4mm depending on oven. Is it ok to run this,this way ? and would it be better contained in plastic trunking. I realise mcb would need downsized. Thanks
 
got any pics for that ,what size is the current feed to the cooker control unit ,you can run it under the base units and come up behind it ,is the oven going in a housing unit or free standing.
 
Just flinging it in under the cupboards is likely to end up with the customer posting it on here asking if it's ok. :D
 
Yes you can install the cable below the kitchen units and it should be fixed. If the cable is less than 50mm from the skin/plinth of the unit it will require additional rcd protection.
 
Thanks westward, nice to get a bit of practical help.
I have to edit your last post. The forums have varying members and banter is part of life on here and whilst some posts on here were not helpful it is best to report them as opposed to responding back.
 

Reply to cable from existing cooker control switch to new oven/grill in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, I'm about to replace our kitchen and one of the upgrades is to install two full size ovens to replace the original twin over under...
Replies
7
Views
1K
Hi All, We have an old Country villa in Spain. The housing electrics were not good so the house recently has been completely re-wired to a good...
Replies
2
Views
745
I have just had my kitchen redone and the kitchen rewired with a new 6mm cable installed for an electric cooker. However I have changed my mind...
Replies
10
Views
2K
Some advise or views would be appreciated. My supply is 100 amp single phase. I purchased my property 3 years ago or so, the owner prior to the...
Replies
29
Views
857
We have a room in the house that was the kitchen. That has been relocated to a different area, so the old kitchen has been sold off and the room...
Replies
2
Views
631

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock