Discuss Cable routing inside a consumer unit in the UK Electrical Forum area at ElectriciansForums.net

First of all, welcome to the forum.

However…

No SPD, they look to be 63A type AC RCD’s, looks to have single 2.5mm cables going into 32A MCB’s

surely this is a wind up?

I can’t see a sparky signing it off and you getting an LABC compliance certificate.
They're type A RCDs.
The single cable is one side of what will be a ring when completed.

My most immediate concern....(of several)
Does this:
View attachment 105842

lead to this:
View attachment 105843

as your diagram seems to imply?
It does, that cable is one end of the kitchen socket ring. The other end of the ring that's also connected to that MCB comes in from the top of the CU.
 
It does, that cable is one end of the kitchen socket ring. The other end of the ring that's also connected to that MCB comes in from the top of the CU.
It's highly dangerous to have a coil of live cable on the floor with bare ends. Final circuits shouldn't be connected up until they are complete and tested.

Also, the other B32 MCB on the left shouldn't have a single 2.5 sq mm cable either as it isn't rated to carry 32 amps. (as mentioned higher up)
 
Wheres your spd?
How much of a gap is there around the cables that enter the top of the cu through that gromit?
Where is the support for the tails (and other cables)?
Wheres your label on the MET?
Why is there a live coil of cable on the floor?
Whos doing notification to labc?
Why is there a 32A mcb serving a 2.5mm radial for 1st floor sockets?
Wheres your test results obtained prior to energising?
 
I expect the 2.5 radial is still looping around the house live until it returns to the CU to complete the ring.
 
It's highly dangerous to have a coil of live cable on the floor with bare ends. Final circuits shouldn't be connected up until they are complete and tested.

Also, the other B32 MCB on the left shouldn't have a single 2.5 sq mm cable either as it isn't rated to carry 32 amps. (as mentioned higher up)

No, that's not the same cable. There are 2 cables coming up through the floor. The coiled cable on the floor is the start of a separate ring and is not connected up or in any way live.

Taken on board the point about the 32A MCB, I was already intending to replace it with the spare 16A.
 
The first thing to do is to switch off those mcbs one at a time, then turn off the CU main switch followed by the isolator.
Then check the main fuse rating if above 63 amp, disconnect the entire CU and take it back to screw fix.
 

Reply to Cable routing inside a consumer unit in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have a doorbell I want to install. The issue is the 16v transformer is designed to sit on a DIN rail. I have a 10 way 17th edition BG Nexus...
Replies
4
Views
904
I was just googling for skeleton boards after reading the last thread and various pictures of consumer units popped up, some wired terribly and...
Replies
6
Views
726
Just looking to see if anyone’s had a similar job or has any other ideas. Got a consumer unit to upgrade, the current one is fitted inside an...
Replies
2
Views
847
Hi all! I'm not a spark but know enough to be able to install off grid solar etc. I've just purchased a new house and have noticed the consumer...
Replies
30
Views
5K
I have a fairly recently installed consumer unit with an RCD, between it and the garden there is another, much older (25yrs?) RCB (big Wylex...
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock