Discuss Cable run for Fixing a double socket on Chimney Breast in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
14
Hi

Would this be allowed : Fitting a double socket to a chimney breast , chased a horizontal run across the chimney breast then to the first corner then along horizontal to about 500mm to meet up with a double socket feed that comes down to a double socket and then it follows that run down into that back box to pick up the feed .

The cable is in a oval plastic conduit and will be just below the surface , the house has RCD protection .

Spike
 
i would come horizontally from existing socket onto chimney brest, then vertically to your new socket. makes the safe zones easier to follow. or....... up from existing socket int ceiling void, then across to chimney and verticall down to new socket.
 
Technically the 500mm you chased horizontally to meet the vertical chase would not be in the zones.
I have drilled diagonally through the chimney breast wall before to make the horizontal chase on the face of the chimney meet the vertical chase on the side. The walls are more than thick enough to avoid going into the chimney cavity quite easily.
 
Thanks for the feedback, just a note , the chimney breast is flush with the wall ! .
Cheers
spike
then either way is compliant.each socket will create a safe zone for the cables.
 
Maybe this will explain it better !

Socket Fireplace.jpg
 
Be careful not to puncture the chimney in any way. Ifs it's not an active chimney now then it may well become active in the future and could leak harmful gases.
 

Reply to Cable run for Fixing a double socket on Chimney Breast in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I'll start by saying - I have absolutely no intention of doing any wiring or anything electrical myself. You get someone professional to do a...
Replies
8
Views
840
Is it possible to install a double socket on a chimney breast that has an active wood burner at the bottom? Looking to mount a TV above the...
Replies
1
Views
3K
Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
2K
Hello All, I have just found out that a family member who is having some Building work done has been advised to insulate above the Kitchen...
Replies
16
Views
808
Hi I've got an new outbuilding that needs power run out to it, the building is very close to the house and the original plan was to run an...
Replies
9
Views
927

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock