Discuss cable run perpendicular to loft joists. in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
57
hi just been to look at a job, have to get a cable accross 4 joists ( perpendicular) now i know drilling loft joists is a no no, the cable run will be in an area of the loft not used for storage and the customer has no intention to board out the loft is there anything wrong with laying the cables accross the joists, neatly and secured under the existing insulation? ( 1.5mm 6amp lighting)
 
yes i know its in the book is that for floor and loft joists ?? im not totally sure it is. i guess it depends on the size of the joist in the loft space.

i cant really see any problem with laying over the joist as in a non traffic area and customer is not boarding the loft
 
ive seen it loads of times, but you should clip to the joists slightly below the top surface, just so no1 does kick them stand on them
 
I'd venture to suggest that going through the odd joist is better, especially if some muppet comes along with boards later and traps the cable between the joist and the board!
 

Reply to cable run perpendicular to loft joists. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, I'm looking to install a new bathroom extractor fan in my bathroom as I have a windowless bathroom and the current one I have installed in...
Replies
13
Views
692
Hi My 4 bed 2 storey house was extended 2 years ago and completely re-wired, but I am having to upgrade the insulation and board out the loft...
Replies
0
Views
1K
Hi all, Have a relatively simple question. Doing a rewire to make a circuit in a single room. My father is a retired spark, so no worries about a...
Replies
7
Views
2K
Hi All. I am wiring a loft conversion and want to avoid covering cables in the insulation. I can clip the cables to the studs on the other side of...
Replies
3
Views
3K
Hi all, Getting the utility room redone at this project house and the misses is absolutely adamant she wants downlights. Couple of reasons for...
Replies
26
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock