Discuss Cable size when burying in the UK Electrical Forum area at ElectriciansForums.net

What is not clear is what that 12% is. If it were under half a meter under/through a wall on a 5m run then probably thermal effect is small, but if any significant length then you would have to de-rate the CCC to that segment as James said.
 
EV car chargers 22kw each x 6
Is your intention 3 on each cable?
Do you mean exactly what you said - 22kw chargers (implying DC to directly charge the batteries) or did you mean 22kw AC charge points which use the charger in the car?
Most people don't every mean "chargers" but as the cable sizing you quoted isn't immediately making sense to me this could be the beginning of a most interesting thread!

(For what it's worth, without doing any maths, Zs, or volt drop etc... my understanding was that a 22Kw charge point on a balanced 3 phase supply draws approx. 32 amps and the one I've seen was installed with 6 sq mm conductors admittedly very close to the supply. )
 
You really need to know what EV chargers you intend to install & if 3 on each cable. You may need to size the cables to allow for future additions of more charge points. Do you intend to charge all points simultaneously? If not, will you be using a management system to monitor & manage the peak building loads without affecting the main use during the day?
 
Also check what the OCPD requirements are, it might be each charger needs its own protection so you would be needing either 6 cables from the DB, one per charger, or a sub-DB at the end to distribute power.

I am no expert on EV chargers but I would be very surprised if 22kW units are not 3-phase, and also need neutral, so you would be looking at 4C cable for the feeds.

Also are the two cables you mention going in separate ducts, or shared duct? Then you have to allow a grouping factor as well as the buried-method de-rating.
 
I am no expert on EV chargers but I would be very surprised if 22kW units are not 3-phase, and also need neutral, so you would be looking at 4C cable for the feeds.
Yes, 22Kw EV charge points are 3 phase. The only one I've seen in the flesh required a neutral.
I almost mentioned the 4th core but thought there was a remote possibility these were DC chargers as 6 of them sounded like a large car park where rapid charging might be required and it would begin to explain the larger cables.
 
Also check what the OCPD requirements are, it might be each charger needs its own protection so you would be needing either 6 cables from the DB, one per charger, or a sub-DB at the end to distribute power.

I am no expert on EV chargers but I would be very surprised if 22kW units are not 3-phase, and also need neutral, so you would be looking at 4C cable for the feeds.

Also are the two cables you mention going in separate ducts, or shared duct? Then you have to allow a grouping factor as well as the buried-method de-rating.
HI

Cables will do into conduit under the ground and be grouped together.
The chargers are 415V, no mention of neutral on data sheet but I'll check with supplier.
 

Reply to Cable size when burying in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Happy New Year all. Quick question regarding cable sizing. I have a 25m run from DB to car charging unit. The 25m run will mean approx 8m is run...
Replies
5
Views
677
Hi everyone, I intend to bury a 240 volt cable from my house to my barn about 7 metres as way. It will be buried under my tarmaced drive which I...
Replies
7
Views
353
Hi , I’m going install a commercial 450mm extractor fan , what size and type of cable should i use ?
Replies
7
Views
447
The electrician that installed my cooker circuit put in 10mm cable with a 32a fuse, a 45a cooker switch and 10mm cable to the backplate for behind...
Replies
23
Views
963
Some advise or views would be appreciated. My supply is 100 amp single phase. I purchased my property 3 years ago or so, the owner prior to the...
Replies
29
Views
931

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock