Discuss Cable sizing calculation in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
18
Happy New Year all.

Quick question regarding cable sizing. I have a 25m run from DB to car charging unit. The 25m run will mean approx 8m is run in the attic, 6m is run clipped direct down and across a wall and the remaining 10-11m will be buried underground in a 2 inch duct to the car charging unit. My calculations tell me I require a 10sq cable. However, whenever I've seen other sparks install a 7kw car charging unit, it's usually a 6sq cable run. Granted the runs would be a bit shorter.

Any thoughts or tips on this please?
 
Quick question regarding cable sizing. I have a 25m run from DB to car charging unit. The 25m run will mean approx 8m is run in the attic, 6m is run clipped direct down and across a wall and the remaining 10-11m will be buried underground in a 2 inch duct to the car charging unit. My calculations tell me I require a 10sq cable.
and what cable will you use ?
 
depending on de-rating factors, it may be possible to do the run in 4mm swa. assuming a 5% voltage drop.
do you want to share your calculations for a double check?
 
depending on de-rating factors, it may be possible to do the run in 4mm swa. assuming a 5% voltage drop.
do you want to share your calculations for a double check?
To be honest James I use an app- Electrical Calculations. It auto calculates the cable size once you enter the specifics/parameters. Voltage, load, PF,
length of run, max volt drop, method of install, ambient temp, conductor, insulation etc. Not good practice I know to be putting my faith in an app for this.

230v, 7.4kw, 0.9 PF, 30m line run, 4% volt drop, I changed the method of install to buried directly in the ground, ground temp of 10° and it suggested a 6sq cable
 

Reply to Cable sizing calculation in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi All, I have a client who is developing a plot of land for a single house. Currently, their 100 amp service cut-out is in a cubicle fed by...
Replies
7
Views
1K
I am an enthusiastic retired engineer rebuilding a barn in France from scratch and am having problems sizing my incoming electrical cables. I have...
Replies
6
Views
2K
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
437
I have a run of cable where 12% is buried in ducts, the rest is on perforated tray, what are the limits on amount of cable buried when sizing cables?
Replies
17
Views
2K
Hi all, looking for some clarification on MCB and cable sizes I need to run for a new kitchen. Cables will run through a combination of...
Replies
0
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock