Hi everyone,

Ive been asked by the customer to supply a 16mx8m metal shed, it will be used as for his hobby of working at old cars it will have 5 circuits,
supply to another out building 50m away with a couple of sockets and 5 lights, prob 20amp be enough
a ring main
lighting circuit 6-8 led lights
roller door
car lift with 3hp motor.
The problem is the shed is 115m away from the house, hes asked me to price for a 63amp and 40amp supply. From my cable calcs a 2-core 16mm swa will have 12.88 volt drop for the 40 amp supply and 20v for the 63amp supply(too much). The calcs for the 25mm swa is 12.68v at 63 amps.
Ive worked out using k1/k2 X S that the armour is ok for the cpc. I will be fitting a 100ma S-type at the house end and driving a spike in at the shed end.
Is there any other factors i need to take into consideration for that run of cable?
Also only looking to use two cores to keep the cost down. Do for a pound what any fool can do for a fiver :)
Thanks in advance.
 
Hi everyone,

Ive been asked by the customer to supply a 16mx8m metal shed, it will be used as for his hobby of working at old cars it will have 5 circuits,
supply to another out building 50m away with a couple of sockets and 5 lights, prob 20amp be enough
a ring main
lighting circuit 6-8 led lights
roller door
car lift with 3hp motor.
The problem is the shed is 115m away from the house, hes asked me to price for a 63amp and 40amp supply. From my cable calcs a 2-core 16mm swa will have 12.88 volt drop for the 40 amp supply and 20v for the 63amp supply(too much). The calcs for the 25mm swa is 12.68v at 63 amps.
Ive worked out using k1/k2 X S that the armour is ok for the cpc. I will be fitting a 100ma S-type at the house end and driving a spike in at the shed end.
Is there any other factors i need to take into consideration for that run of cable?
Also only looking to use two cores to keep the cost down. Do for a pound what any fool can do for a fiver :)
Thanks in advance.
What about the 3 phase car lift , need more than 2 cores for that jobby Mate
 
Why does the customer want 2 supplies? Wouldn't it be better to just supply a 100A circuit to where he wants or have I misread something?
What size is the main fuse in the house seeing that you are taking the supply from this?
 
Why does the customer want 2 supplies? Wouldn't it be better to just supply a 100A circuit to where he wants or have I misread something?
What size is the main fuse in the house seeing that you are taking the supply from this?
It's one or the other 40 or 63 due to cost/length of cable. Wish the shed was closer lol.
 
Although the customer says he wants a 40 or 63 Amp supply, what has he based this on? As this is a guy in his shed he can only use one machine at a time plus lights, so off the top of my head I would say a 20 Amp supply would be enough. If it was a commercial workshop with a couple of people working in it that would be different.
Identify the individual loads and discuss with your customer what is likely to be used at any time. Hopefully you can get the max current down which should help with the volt drop calcs.
 
Although the customer says he wants a 40 or 63 Amp supply, what has he based this on? As this is a guy in his shed he can only use one machine at a time plus lights, so off the top of my head I would say a 20 Amp supply would be enough. If it was a commercial workshop with a couple of people working in it that would be different.
Identify the individual loads and discuss with your customer what is likely to be used at any time. Hopefully you can get the max current down which should help with the volt drop calcs.
Its a forever home, hes got a few sons so within 5-10 years there could be a few ones down working in it. Its the kind of job you want to do once, The out buildings is 4 stables with a big paddock area (not in use). I know we cant plan to far in front. but with the hassle of digging a span that length in i dont want to leave him short in the future. It was me that suggested either a 40a or 63a.
Il price for the two and let him decide.
Iv never designed a sub-mains that length, just wanted to hear from others who has.
 
But for 1 cable over 115m at 63A, you are looking at 50mm SWA to get below the 3% voltage drop. ( 2.55%)
For 1 cable over 115m at 40A, you are looking at 25mm SWA to get the 3% voltage drop.
Will 40A be enough with the car lift and everything else?
So what size is the main fuse in the house?
 
you can wing the 3% for lighting if you fit all LED lights. this could allow a 25mm SWA for > 40A.
 
But for 1 cable over 115m at 63A, you are looking at 50mm SWA to get below the 3% voltage drop. ( 2.55%)
For 1 cable over 115m at 40A, you are looking at 25mm SWA to get the 3% voltage drop.
Will 40A be enough with the car lift and everything else?
I was going of the 6% in part (ii) my mistake. The 3 horse motor will run on a 16a d type. The guy who supplied the lift said it will pull 32a on start up.
Theres a 100a main fuse in the house.
The lift isnt going to be used all the time more hand tools, compressors, grinders and lights so bare minimum 40a. Would like to have left it with 63a though.
Theres an 11kv overhead with a pole about 10m from the shed. but the cost to fit a transformer with a new supply will far outweigh a 100m run of swa.
 
Is there any other factors i need to take into consideration for that run of cable?
If the supply is TN-C-S and you don't TT the remote building then you need 10mm copper equivalent for the CPC.

For 2-core SWA that only happens by time you get to 70mm, expensive!

If smaller SWA (but above 10mm) it can be cheaper to run a 10mm coper CPC in parallel with the SWA.
 
If the supply is TN-C-S and you don't TT the remote building then you need 10mm copper equivalent for the CPC.
I must admit this sentence has perplexed me, and I'm probably missing something.
If we were talking about the main earthing conductor for the installation at the house I'd get it.
But we are talking about a circuits CPC here aren't we, so doesn't it just have to meet 543.1.3, and be equal to line conductor if less than 16mm sq?
 
If the supply is TN-C-S and you don't TT the remote building then you need 10mm copper equivalent for the CPC.

For 2-core SWA that only happens by time you get to 70mm, expensive!

If smaller SWA (but above 10mm) it can be cheaper to run a 10mm coper CPC in parallel with the SWA.
but only if there are extraneous parts in the garage. ?
 
I must admit this sentence has perplexed me, and I'm probably missing something.
If we were talking about the main earthing conductor for the installation at the house I'd get it.
But we are talking about a circuits CPC here aren't we, so doesn't it just have to meet 543.1.3, and be equal to line conductor if less than 16mm sq?
think he means as a bonding conductor. see post #15.
 
If the supply is TN-C-S and you don't TT the remote building then you need 10mm copper equivalent for the CPC.

For 2-core SWA that only happens by time you get to 70mm, expensive!

If smaller SWA (but above 10mm) it can be cheaper to run a 10mm coper CPC in parallel with the SWA.
Its a TT system at the house and will be made TT at the shed, Im not using the armour as a cpc for the shed, only for the sub-main cable which will be protected by a 100ma s-type RCD. I will install a spike at the shed.
 
Its a TT system at the house and will be made TT at the shed, Im not using the armour as a cpc for the shed, only for the sub-main cable which will be protected by a 100ma s-type RCD. I will install a spike at the shed.
Is there any chance the house will become PME (TN-C-S) at any time? If not, then I would use the armour to link both as well as an earth rod. Generally the lower the Ra the better and multiple earths allow less chance of a single point of failure.

Will the sub-main be off the supply (i.e. split tails and the 100mA delay-RCD as an isolator) or is it coming off the house CU that already has a 100mA delay RCD up-front? Fine in both cases, but ideally all final circuits at the out building on 30mA RCD/RCBO so you don't lose the lot on a fault.

If it is planned as a workshop you might also want to consider some LED lighting with built-in emergency battery, that way you don't end up plunged in to darkness with tools spinning, etc, if the light supply goes off for any reason (including supply interruption).
 

Reply to Cable size in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi guys, I have supplied my Shed with a 6mm SWA cable into a nice consumer unit. In there I have a 6Amp MCB for the lights and a 16 A supplying a...
Replies
25
Views
948
A friend of mine wired a 10mm 3 core armoured cable to his shed before I got involved and wired it himself already. He wants make it an air bnb...
Replies
8
Views
876
Client currently has a DB in his outhouse. It feeds a pool pump and an air source heat pump. It is currently being supplied using a 4mm T&E cable...
Replies
9
Views
624
Hi All, I have a client who is developing a plot of land for a single house. Currently, their 100 amp service cut-out is in a cubicle fed by...
Replies
7
Views
1K
Hi All, Im quoting to install an EV charger (Dont worry - fully registered, but only been 2 weeks so i'm still picking bits up). Consumer unit...
Replies
1
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock