Hi, searched but still niggling problem need help on...

Installation: -
4mm earth to earthing electrode (rod) Ra 42ohm
Zdb 33ohm
1361 60A main fuse
16mm tails
cant get acceptable result for using adiabatic as disconnection time too high (higher than 5 secs with that Zs reading)
no frontline RCD protecting tails.
What would the minimum bonding size be? (2mm therefore 4mm wiring?)
 
You will not disconnect on the OCPD with practically all TT installations due to the significant Ra, you would be looking at having RCD here for fault protection, not just for additional protection against shocks from contact with L & Earth.

While you could attempt to compute the adiabatic limit from the RCD's disconnection time and the PFC to Earth, in reality you are looking at least at 4mm for this (as it is unlikely to be mechanically protected all the way, see 543.1.1).

But as you can see, this means you have no protection for a L-CPC fault before any RCD or RCBO, so you must have great care that cannot occur, for example not just sheathed tails (as normally used) but also a proper gland to clamp the cables as they enter the CU to reduce the risk of movement or strain on the tails causing them to come out of the incomer switch and/or cutting against the CU body.

Of course, you must have RCD protection on every circuit. Traditionally that was an up-front RCD (ideally something like 100mA delay) and then whatever instant 30mA RCD protection is needed. But a dual RCD board or all RCBO is also complaint. Just absolutely no non-RCD circuits as your Ra is too high for practically all common OCPD.
 
You will not disconnect on the OCPD with practically all TT installations due to the significant Ra, you would be looking at having RCD here for fault protection, not just for additional protection against shocks from contact with L & Earth.

While you could attempt to compute the adiabatic limit from the RCD's disconnection time and the PFC to Earth, in reality you are looking at least at 4mm for this (as it is unlikely to be mechanically protected all the way, see 543.1.1).

But as you can see, this means you have no protection for a L-CPC fault before any RCD or RCBO, so you must have great care that cannot occur, for example not just sheathed tails (as normally used) but also a proper gland to clamp the cables as they enter the CU to reduce the risk of movement or strain on the tails causing them to come out of the incomer switch and/or cutting against the CU body.

Of course, you must have RCD protection on every circuit. Traditionally that was an up-front RCD (ideally something like 100mA delay) and then whatever instant 30mA RCD protection is needed. But a dual RCD board or all RCBO is also complaint. Just absolutely no non-RCD circuits as your Ra is too high for practically all common OCPD.
There is no absolute requirement in BS7671 that every circuit must have rcd protection with a TT earthing system.
 
You will not disconnect on the OCPD with practically all TT installations due to the significant Ra, you would be looking at having RCD here for fault protection, not just for additional protection against shocks from contact with L & Earth.

While you could attempt to compute the adiabatic limit from the RCD's disconnection time and the PFC to Earth, in reality you are looking at least at 4mm for this (as it is unlikely to be mechanically protected all the way, see 543.1.1).

But as you can see, this means you have no protection for a L-CPC fault before any RCD or RCBO, so you must have great care that cannot occur, for example not just sheathed tails (as normally used) but also a proper gland to clamp the cables as they enter the CU to reduce the risk of movement or strain on the tails causing them to come out of the incomer switch and/or cutting against the CU body.

Of course, you must have RCD protection on every circuit. Traditionally that was an up-front RCD (ideally something like 100mA delay) and then whatever instant 30mA RCD protection is needed. But a dual RCD board or all RCBO is also complaint. Just absolutely no non-RCD circuits as your Ra is too high for practically all common OCPD.
I don't think a dual rcd board is recommended on a TT Pete due to the internal tails.
 
True but pedantic.

Very few MCB will disconnect on that sort of Zs, even 3A B-curve (14.6 ohm) or 3A fuse (15.6 ohm), hence it becomes necessary.
In relation to the OPs readings true but nevertheless it is correct. A 5A BS3036 fuse can be pushed to 9.10 ohm and in the days of mixed disconnection times 16.8 ohm.
 

Reply to Calculate bonding sizes TT in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

This is a question (or discussion probably) regarding selecting the main earthing conductor, and subsequently the main equipotential bonding...
Replies
26
Views
6K
Doing an EICR on a top floor flat recently and run into an issue I often do - which is judging imperial sizes when they are larger than the...
Replies
22
Views
3K
Afternoon all, Just trying to clear something up, going through regs book at present. Basically have got a TNC-S/PME installation, 16mm tails...
Replies
23
Views
15K
My assessor said that the minimum CSA for a Main earthing conductor for a TT was 16mm. I questioned this as I thought it was 4mm. Regulation...
Replies
30
Views
11K
Hello All, Tying my brain in knots trying to work out if this earth is ok: TT system with 100mA RCD on tails Tails then go into an isolator with...
Replies
25
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock