Discuss Calculated Zs on an EICR in the UK Electrical Forum area at ElectriciansForums.net

TJC1

-
Reaction score
6
Got asked to carry out and EICR on a doctors surgery (NHS)

On the previous inspection done 5 years ago, they stated under limitations.. The Zs reading of each circuit has been calculated.

In theory if you have a Ze + R1 + R2 then yes you would get the result, but isn't it still good practice to do your Zs test?
 
Personally speaking I always prefer to measure Zs as this is the only test that confirms the complete circuit including protective devices. There’s always a possibility that you can have a high resistance accross a device that would result in a high impedance at the end of the circuit. This will never be found by calculation.
 
Most circuits that are not protected by an RCD are buried in the wall less than 50mm. Would you make a note of this C3 for every circuit?
 
Got asked to carry out and EICR on a doctors surgery (NHS)

On the previous inspection done 5 years ago, they stated under limitations.. The Zs reading of each circuit has been calculated.

In theory if you have a Ze + R1 + R2 then yes you would get the result, but isn't it still good practice to do your Zs test?
Why wouldn’t you do a zs test.
 
The regulations also state that zs can be obtained by other methods than direct measurement so technically it’s not against regulations if you don’t do a direct measurement.
As it’s an EICR I do direct measurement and don’t bother with the R1+R2 method
I use a wander lead connected to the MET and connect to exposed conductive parts(lights and the like) to verify they are connected to earth
 
Last edited:
written by suits at a desk, instead of us poor sods in the real world.
Is it not actually better for various reasons. You can't do a live test for zs without bonding connected which will give you a lower value. However building works may permanently remove that parallel path.
If you use ze + r1 + r2 you get the highest possible value which will be more resilient.
No?
 
it's a C3 all day long. only way you could justify a C2 is potential danger from a numpty nailing or screwing the cable.if it's within prescribed zones, then numpty deserves whatever he gets.
 
It isn't an authoritative source though Code designation should be judged from knowledge, experience and any factors which are present on the day. You should not need a guide to steer you through an EICR and if you do maybe you need to question your competence for the task you are undertaking.
 
The code breaker book advises a C2 code for tails that are not the minimum required 25mm.
I mean where in bs7671 states that tails must be 25mm?
What if you have 16mm tails? Why is that a C2 if they are acceptable for the load they are connected to and satisfy the requirements for fault protection?
 

Reply to Calculated Zs on an EICR in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, I did my first EICR on a TT system today and the Zs was a lot higher than Ze+R1+R2 on everything. Zs was around 3.5 ohms on all of the ring...
Replies
10
Views
1K
OLDBOY
O
Hi all Done a EICR on a flat which had the link fuse in the service head .. had an earth wire coming off the orange cable to an earth block...
Replies
16
Views
825
So I’m doing my level 3 design project at the moment, and I’m on the question where you do all the calculations on each circuit, I’ve taken the...
Replies
3
Views
1K
I have been asked to look at this report as the customer has been given (in their words) 'A very high quote plus VAT'. It doesn't look well...
Replies
5
Views
613
Evening everyone, I was taught when carrying out Zs testing to test both L-PE and L-N and record the highest result of the two tests for my Zs...
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock