Discuss Calculation submain cables in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
0
Hi. Im looking for some advice when calculating submain cables.
Basically there is a new connection of 80Amps that is to be used for a dwelling and a small workshop. I had thought taking to a feeder box with one submain and then two feeds away into the buildings.
A direct run from dno to feeder box is 70m a preferred run would be 100m
25m into dwelling.
50m into small workshop.

I was told the volt drop wpuod need to be 3% from dno to end of lighting circuits.

My calculations are showing.
100m 95mm swa
25m 35mm swa
50m 35mm swa

But other firms have told the customer that they would use 25/35mm swa for the entire run due to diversity.

Even with divesity of the dwelling im coming up to about 45A for that alone.

Any advice would be most appreciated.

Thank you
 
Your volt drop theory is correct it is calculated from source to the end of each final circuit, people often use a rule of thumb of 2% for submains.
 
I've always advised the customer to spend a few more £££s on the submain than the calculations required. It can pay dividends further down the line when any additions are made to the final circuits .
 
If it is TT then you can use the armour of any of them as CPC but will almost certainly need an up-front delay RCD at the sub-main feed point to allow disconnection on a fault.

If TN-C-S then the bonding size of (typically) 10mm copper equivalent can be an issue for many SWA cables as it translates in to about 80mm of steel, you might find it significantly cheaper to run a parallel 16mm CPC or whatever instead of going 3C if you are looking at 95mm cable, but again check Zs levels as that might also push you in to needing up-front delay RCD fault disconnection which might negate a lot of any cost savings.

Aiming for 2-3% VD on the feed makes sense, though that is on the realistic max load which may be less than the OCPD size. If future use is not known then sizing based on the OCPD makes sense. If you are running big loads for a lot of the time then it can pay off in terms of electricity savings vs. copper price over 5 years or so to size the feed bigger, but for many domestic cases the usage duty cycle (and so I2R losses) are unlikely to make it worth pushing down to 1-2% or below.

These days the VD on domestic LED lighting circuits should be very small so meeting just below 3% of the feed ought to be enough, but as it is expensive to do they really need to think forward to anything they might want in the future and if that could push for a 3P supply then you might be better going with something like 4C 50mm paralleled for single phase now, instead of 2C 95mm, if it might meed the drop for a future 3P supply as well without needing a cable change.
 

Reply to Calculation submain cables in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Happy New Year all. Quick question regarding cable sizing. I have a 25m run from DB to car charging unit. The 25m run will mean approx 8m is run...
Replies
5
Views
668
Hi guys, Can I ask you a DIY question? I'm refurbing a detached garage and adding a garden building. Garage currently has a submain supplied by...
Replies
1
Views
803
Hi, thanks for reading this. Ive been asked to look at a job where the DNO connection (single phase 80A TT) is a long run to the final circuits...
Replies
4
Views
274
Hi everyone, A diversity question concerning 2 consumer units fed from 100amp DNO supply Background, So I have an 18th Ed compliant consumer...
Replies
9
Views
2K
Hi all, Hope you're keeping well I'm currently wiring a small commercial premises. 3 phas incoming supply, 16sq cables As it is in an urban...
Replies
3
Views
292

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock