i,m just wondering how to calc. volt drop on an install like this. assuming 1 or 2 radial circuits, the load is taken at varying points, i.e. the load at the end of a run is not the total load. (only 10A if each van has a 10A supply) so would you use 10A for the full cable length, and calculate say at 50% of the length at say 30A ( allowing na bit of diversity)
On a radial circuit, your biggest loading is at the first point, 9 x caravans at 10a =90A. Second Point 8 x 10A =80A , and so on. To conduct a diversity exercise you will need some experience of such caravan installations, which i'm sorry to say i don't have. Maybe someone here on the forum, will be able to help on that score for you....
The volt drop calculation is similar to those or a row of lights so distance x load at each point along the circuit then combine the totals