Can a 50a MCB be fitted into that space ?

Discuss Can a 50a MCB be fitted into that space ? in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
3
Screenshot_20210104_092558_com.whatsapp.jpg
 
It will fit into the space outlined in orange, but there are other considerations. what will it be used to power, and does the curcuit require RCD protection?als bear in mind that it should be same make and type as existing.
 
It will fit into the space outlined in orange, but there are other considerations. what will it be used to power, and does the curcuit require RCD protection?als bear in mind that it should be same make and type as existing.
Hi thank you yeah it's the same make and it's for electric shower I was concerned that the 80a RCD already has 70a worth of switches next to it already or is it possible to but the 50a alongside them
 
What's the kW rating of the shower? and bear in mind that the 3 other breakers' values are max. rating. the actual load willbe much less most of the time.
 
you'd just get away with 6mm cable on a 40A MCB if no insulation on the cable route. but if installing the cable go for 10mm on a 50A.
 
OK.part p is a building reg. whereby certain works need to be notified to building control at local council. any work within a special location (bathroom) falls under this. your guy will need to be a member of NICEIC or one of the other similar organisations.
 
If you have a new Wylex MCB don't assume it will fit the NSB range hasn't been manufactured for a good number of years
Wylex told me I had to replace all the breakers in their CU when we ran a new circuit for a cooker range - 2020, because the existing were BSBs.
 

Reply to Can a 50a MCB be fitted into that space ? in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock