Can I confirm how to test for and how to find a borrowed neutral?

Discuss Can I confirm how to test for and how to find a borrowed neutral? in the UK Electrical Forum area at ElectriciansForums.net

HappyHippyDad

-
Esteemed
Arms
Supporter
Reaction score
5,657
During some testing I found a N-E IR fault on the kitchen lights of 0.1Mohms. I also found a N-E IR fault on the ring sockets, again 0.1Mohms.

This could have been a coincidence, but I disconnected both neutrals from the neutral bar (i.e the kitchen lights and sockets) and tested between them. They showed continuity (0.97 ohms). Just FYI, there was no continuity with these neutrals to the neutrals of the other circuits.

This is a dual RCD board. K lights and sockets on the same side.

Does the fact the neutrals showed continuity mean this is a borrowed neutral? I have not come across continuity between neutrals before. Is this the correct test for them? Does it actually mean they are connected together somewhere, or am I missing other possibilities?

Also, as the neutrals have been connected together somewhere in the house between these 2 circuits, how do I find this join? The house is full of shoddy DIY alterations. I would like to offer at least a guess as to how you find this join, but for the life of me I cannot think of a way.
 
This N-E test stuff is all old news, see my post #19. There is unusually low insulation resistance between neutral and earth but not a short, so whilst it needs finding it's not the reason that the two neutrals show a hard short together. It might be further evidence of some cables nailed together or co-located with the N-N problem though.
 
In your example. If the line had been taken from a switch on the lighting circuit and the neutral from a nearby socket, how would that show continuity between neutrals?

Sorry, that was my mistake, I didn't fully think that one through!

I was at the time bored at work watching the special effects people (plumbers) ruin a perfectly good stage floor with their rain effects.
 
Last edited:
Ive had 2 o these no so long ago.
One was a conservatory light where they had wired live from a nearby two way switch and taken the neutral from the socket below.
Second was kitchen under unit lights same wiring.
Id be looking around trying to spot the red flags first, opening some accesories should help you identify the culprit.

Good luck.
 
This is different though. It's not a line from one circuit paired with a neutral from another, it's two different neutrals connected together. It's not something you would do even as a bodge and might be a true fault e.g. a screw through two cables.
 
This is different though. It's not a line from one circuit paired with a neutral from another, it's two different neutrals connected together. It's not something you would do even as a bodge and might be a true fault e.g. a screw through two cables.
Absolutely possible, but just seems so unlikely. A screw passing perfectly through 2 cables, missing the earth on both (which is probably centred in the middle of the cable) and touching both neutrals.
I suppose it has to happen one in a million times, so perhaps this is it. I'd rather have won the lottery!
 
Absolutely possible, but just seems so unlikely. A screw passing perfectly through 2 cables, missing the earth on both (which is probably centred in the middle of the cable) and touching both neutrals.
I suppose it has to happen one in a million times, so perhaps this is it. I'd rather have won the lottery!
I had a lighting cable, a twin and earth used as a pair of strappers between 2 way switching, damaged by a nail for a dado rail. It nicked one of the strappers and caused a live to earth fault. Only the strapper was nicked, not the cpc. Fault finder was complicated by which where the two switches were operated.
 
It's proving difficult getting a date to do the fault finding, so I'm afraid there won't be an update any time soon. I will update though when I've been back.
 
This is different though. It's not a line from one circuit paired with a neutral from another, it's two different neutrals connected together. It's not something you would do even as a bodge and might be a true fault e.g. a screw through two cables.
I dont think so! Keep taking the pills if you think a screw has gone through 2 different cables. Im assuming you dont do much domestic stuff.
 
I dont think so! Keep taking the pills if you think a screw has gone through 2 different cables. Im assuming you dont do much domestic stuff.
What he means is there are two different scenarios:
A) no neutral there at all so one is stolen from elsewhere (like your conservatory light example)
B) two neutral conductors from different circuits are joined (what this thread is about and not really a borrowed neutral. All my ideas for what we could call this don’t get past the language filter….
 
I dont think so! Keep taking the pills if you think a screw has gone through 2 different cables. Im assuming you dont do much domestic stuff.
I've seen where someone has put two cables one on top of each other to save on clips, notched in under floorboards, so it's certainly possible.
 
Last edited:

What he means is there are two different scenarios:
A) no neutral there at all so one is stolen from elsewhere (like your conservatory light example)
B) two neutral conductors from different circuits are joined (what this thread is about and not really a borrowed neutral. All my ideas for what we could call this don’t get past the language filter….
That is more of an interconnection than a borrowed neutral IMO
 
Last edited:
A pair of cables running along a ceiling joist could both get penetrated.
Hanging a light fitting, if you used long screws and only caught the edge of the joist you could easily cause an N-N short, and maybe also cause a resistance to the CPC at the same time.

The same goes for cables in partitions.


A bit more info on the type of house/size etc maybe of help.
 
Well, I must apologise as I shall not be returning to the customer, so I will not be able to update. I've just had the most odd conversation with him on the phone and he does not want me back. Bit shocked as that hasn't happened before. As in the opening post, he was a very difficult man to deal with but I wasn't expecting that.

His reasons were that I miss diagnosed a faulty cooker and I left the loft lights on!

I'm not a 100% sure I didn't miss diagnose the cooker. The cooker itself showed 0.1Mohms N-E. Is this perhaps acceptable for some cookers? Its an older looking rangemaster. Even so, bit harsh!

Happy not to be going back though, he was a very un pleasant man and shockingly rude to his very pleasant wife.

Oh yes, and he isn't going to pay for the 2 hours fault finding or fixing his 3 kitchen lights. I will not be going to the small claims for a £100 and shall take it on the chin, albeit a little grumpily :)

The neutral problem will remain and we shall never know!!!
 
Well, I must apologise as I shall not be returning to the customer, so I will not be able to update. I've just had the most odd conversation with him on the phone and he does not want me back. Bit shocked as that hasn't happened before. As in the opening post, he was a very difficult man to deal with but I wasn't expecting that.

His reasons were that I miss diagnosed a faulty cooker and I left the loft lights on!

I'm not a 100% sure I didn't miss diagnose the cooker. The cooker itself showed 0.1Mohms N-E. Is this perhaps acceptable for some cookers? Its an older looking rangemaster. Even so, bit harsh!

Happy not to be going back though, he was a very un pleasant man and shockingly rude to his very pleasant wife.

Oh yes, and he isn't going to pay for the 2 hours fault finding or fixing his 3 kitchen lights. I will not be going to the small claims for a £100 and shall take it on the chin, albeit a little grumpily :)

The neutral problem will remain and we shall never know!!!

Sounds like you're better off out of it.
 
It would be brilliant if the next sparks he calls happens to be a member on here.....
Personally I'd take great delight in telling him this is a tricky job and needs an expert - there's a guy I know that specialises in this kind of thing, probably the only guy for miles around that stands any chance of working it out for you....and then give him HHD's number....!
 
Well, I must apologise as I shall not be returning to the customer, so I will not be able to update. I've just had the most odd conversation with him on the phone and he does not want me back. Bit shocked as that hasn't happened before. As in the opening post, he was a very difficult man to deal with but I wasn't expecting that.

His reasons were that I miss diagnosed a faulty cooker and I left the loft lights on!

I'm not a 100% sure I didn't miss diagnose the cooker. The cooker itself showed 0.1Mohms N-E. Is this perhaps acceptable for some cookers? Its an older looking rangemaster. Even so, bit harsh!

Happy not to be going back though, he was a very un pleasant man and shockingly rude to his very pleasant wife.

Oh yes, and he isn't going to pay for the 2 hours fault finding or fixing his 3 kitchen lights. I will not be going to the small claims for a £100 and shall take it on the chin, albeit a little grumpily :)

The neutral problem will remain and we shall never know!!!
Better off rid of him.

I'm confused though, 0.1M Ohms N-E Fault on sockets, lights and the cooker as well?
 
If anything is likely to be giving a 0.1 meg fault it's the cooker. But clearly HHD tested around the lighting and socket circuits carefully, hence discovering the interconnection between them, so it seems most unlikely that he mis-identified which circuit(s) had low IR. I agree it's a bit peculiar.

The cooker itself showed 0.1Mohms N-E. Is this perhaps acceptable for some cookers? Its an older looking rangemaster.

It's entirely possible due to moisture in elements that don't get used often. The figure is likely to be very variable. I bet if you turned all the rings and oven on for 30 minutes, it would go down first, maybe trip the RCD, then up and away into the megohms as the moisture dissipates, only to fall again over time. Whether that constitutes a fault or a pathology of sheathed heating elements is a matter of semantics. Of course it could also be a 'real' fault like charred insulation but that would be a rare exception.

Keep taking the pills if you think a screw has gone through 2 different cables. Im assuming you dont do much domestic stuff.
I haven't touched domestic for 25 years, but I did see this happen once. Cooker circuit and ring under capping in a chase badly out of safe zone, cupboard fixing screw had connected (IIRC) the ring line to the cooker neutral.

I'm sad that we won't get to hear the resolution and that you won't get the satisfaction of rectifying it. One of the things I found when I often used to get hired as a specialist fault-finder, was that I would go into a job subconsciously expecting an endorphin buzz at the end of it. If that didn't happen, e.g. because we couldn't get access or it was a 2-minute fix which the guy on the spot should have dealt with, it would dent my enthusiasm for a while.
 
Sorry, I posted a little too quickly. The figure of 0.1M ohms was for the interconnected sockets/lights. This figure sprang to kind when I was posting regarding the cooker, because it was imprinted on my brain regards the sockets/lights.
I can't find my results now, but I believe the cooker results were lower, how much lower I just can't remember.
 
Well, I must apologise as I shall not be returning to the customer, so I will not be able to update. I've just had the most odd conversation with him on the phone and he does not want me back. Bit shocked as that hasn't happened before. As in the opening post, he was a very difficult man to deal with but I wasn't expecting that.

His reasons were that I miss diagnosed a faulty cooker and I left the loft lights on!

I'm not a 100% sure I didn't miss diagnose the cooker. The cooker itself showed 0.1Mohms N-E. Is this perhaps acceptable for some cookers? Its an older looking rangemaster. Even so, bit harsh!

Happy not to be going back though, he was a very un pleasant man and shockingly rude to his very pleasant wife.

Oh yes, and he isn't going to pay for the 2 hours fault finding or fixing his 3 kitchen lights. I will not be going to the small claims for a £100 and shall take it on the chin, albeit a little grumpily :)

The neutral problem will remain and we shall never know!!!
As a professional civil engineer he would expect to be paid for his services and similarly so should you. At the very least send him a bill spelling out the work and cost with your bank details and terms for settlement eg within x days of date of bill. He is trying to brow beat you in area of engineering he is incompetent and unqualified. And then follow up with a polite phone call after x days. You are not a charity. What is the make and reg of car on their drive?
 
During some testing I found a N-E IR fault on the kitchen lights of 0.1Mohms. I also found a N-E IR fault on the ring sockets, again 0.1Mohms.

This could have been a coincidence, but I disconnected both neutrals from the neutral bar (i.e the kitchen lights and sockets) and tested between them. They showed continuity (0.97 ohms). Just FYI, there was no continuity with these neutrals to the neutrals of the other circuits.

This is a dual RCD board. K lights and sockets on the same side.

Does the fact the neutrals showed continuity mean this is a borrowed neutral? I have not come across continuity between neutrals before. Is this the correct test for them? Does it actually mean they are connected together somewhere, or am I missing other possibilities?

Also, as the neutrals have been connected together somewhere in the house between these 2 circuits, how do I find this join? The house is full of shoddy DIY alterations. I would like to offer at least a guess as to how you find this join, but for the life of me I cannot think of a way.
Please ensure that your IR test is to the Lighting Switch and NOT through their loads…!!!!!

Unless of course you’ve disconnected ALL DC down lights, Flori units, etc etc.

This will otherwise go badly wrong, and resistance tests.
 

Reply to Can I confirm how to test for and how to find a borrowed neutral? in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock