Discuss Can I use a 3 pole isolation switch as a basic trigger switch? in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
1
C55705BF-EE23-4E10-8D10-6BC758E77B4D.jpeg

Hello all, a little help would be much appreciated. I would like my extractor fan to have its own trigger switch, not dictated by the bathroom light switch. However, I’d like that switch to have an indicator flag. I’ve seen the ones on tlc but these are a 3 pole isolation switch. How could this be wired as purely a pull cord trigger switch? Many thanks
 
as you'e drawn it, looks OK. with the 3 pole isolator left in the ON position, all you need is a pull cord lighting switch to switch the fan on. switching off the pull cord, the fan will overrun according to the timer setting. you canperhaps drill the pull cord switch cover and fit a neon .
 
Cheers.
Is like to use the following switch as the pull cord trigger-due to the flag indicator.
129EC2B6-0F6A-499C-9FB8-800AF173960E.jpeg

Any issues in using another 3 pole isolation switch you reckon? Switched live and live, as long as connected in the same line, opposite terminals should provide that on/off....
 
For a normal rather than 3 pole switch you will need a pullswitch with a neon as otherwise you will have no way of knowing whether the trigger switch is in the on or off position, for example if someone comes to the bathroom and finds the fan already running. Crabtree do a 16a DP P/S with a neon that I use in these situations. An alternative is to use a retractive switch as the trigger although this will really need to be outside the bathroom,
 
you will need a N for the neon unless....you connect the neon across L and S/L. then the neon will be ON when switch is OFF, and vice versa. this method was used some while ago by MK on light switches to make them easy to find in the dark. iirc, the neon was green and had a lear lens in front of it. so the switch, when off, glowed in the dark.
 
Cheers.
Is like to use the following switch as the pull cord trigger-due to the flag indicator.
View attachment 55801
Any issues in using another 3 pole isolation switch you reckon? Switched live and live, as long as connected in the same line, opposite terminals should provide that on/off....

Yes you can use that as your trigger switch, there is no problem with that.

Do you really want an overrun on a fan with its own switch? Normally if the fan is on a seperate switch you wouldnt have the overrun or seperate 3 pole isolator.
[automerge]1581871684[/automerge]
For a normal rather than 3 pole switch you will need a pullswitch with a neon as otherwise you will have no way of knowing whether the trigger switch is in the on or off position, for example if someone comes to the bathroom and finds the fan already running.

That's why the OP wants to use the three pole switch, it has a mechanical indicator to show the position.
 
I take it that would be back to just having the live and switched live going to it....no other gotchya’s.....??
Thanks!!
Yes, the fan will of course only run for the time delay set in the fan.
this method was used some while ago by MK on light switches to make them easy to find in the dark. iirc, the neon was green and had a lear lens in front of it. so the switch, when off, glowed in the dark.
That's an MK K3041 neon plateswitch locator, if you ever need one. They are not effective after the painter has painted around all the switches.
 

Reply to Can I use a 3 pole isolation switch as a basic trigger switch? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

D
Hi, I have received conflicting advice about Main Isolator Switches and would appreciate forum member's help to plan a way ahead. Looking to the...
Replies
5
Views
2K
Deleted member 155212
D
This could possible have been a poll, but really just opening up for suggestions and feedback on where folks think an isolation switch for an...
Replies
12
Views
3K
Hello, I'm replacing standard light switches in my hall and landing with touch switches (not smart, just touch on/off) like these from Amazon...
Replies
7
Views
683
D
Hi, I have received conflicting advice about Main Isolator Switches and would appreciate forum member's help to plan a way ahead. Looking to the...
Replies
0
Views
1K
Deleted member 155212
D
Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock