Discuss Can Metrel EasiTest carry out Earth Rod resistance test on TT System? in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
2
Hi,

I have a truck container cafe with a floating generator for power.
I am fitting an earth spike to the generator and also an earth spike to the steel container. I then need to measure the TT system i have created but i only have a Metrel easitest.. Will the tester do the job and if so how do i carry out the test..

Cheers
Tj
 
There
Why on earth are you setting this up as a TT system?
Normal practice is to use TNS for generators

There is only one source of supply, from this floating earth generator. My idea is to make the earth potential belt and braces by adding earth spikes... Can you explain what you mean by creating a TNS please.
 
Hi,

I have a truck container cafe with a floating generator for power.
I am fitting an earth spike to the generator and also an earth spike to the steel container. I then need to measure the TT system i have created but i only have a Metrel easitest.. Will the tester do the job and if so how do i carry out the test..

Cheers
Tj
Even if you did this ,you would not have created a TT system. To create a TT system the earth electrode at the generator end would need to be connected to one of the winding ends to be referenced. What you are describing , would still be a form of electrical separation but with 2 x pointless earth electrodes in the ground.
 
Last edited:
There


There is only one source of supply, from this floating earth generator. My idea is to make the earth potential belt and braces by adding earth spikes... Can you explain what you mean by creating a TNS please.

So you are planning on connecting a floating generators chassis to earth rods? Surely that would increase the chances of serious injury resulting from a second fault?

To have a TT or TNS system you would need the neutral point connected to earth at the generator. To make it TT you would then have no earth conductor from the generator to the load but rely entirely on the return path from one earth rod to the other.
For TNS you connect the neutral point to earth at source and have an earth conductor going to the load.
 

Reply to Can Metrel EasiTest carry out Earth Rod resistance test on TT System? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Has anyone here got experience of doing a soil / earth resistance survey for the design of a large-ish site? We might be looking at a fenced area...
Replies
1
Views
427
Carrying out a EICR in a commercial setting. In the main intake room the DNO supply comes in and it states clearly this is a PME system. 5 years...
Replies
5
Views
1K
Hi How do i access the earth rod to service it, where abouts will it be located and does a tt system have upfront rcds which will be probably in...
Replies
3
Views
990
Hi all, Would like some advice on the below. Context: Rural French domestic installation TT system Earth rod is situated inside the property...
Replies
6
Views
1K
Hi Guys, hopefully someone will know the answer. Testing an install on a (domestic) PME system I have a garage consumer unit supplied from one of...
Replies
17
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock