Discuss Can someone help? in the UK Electrical Forum area at ElectriciansForums.net

You have Ze and you have R1+R2
Ipf at the end of the circuit (not normally considered in calculation) is Uo/Zs.
Zs = Ze+(R1+R2)
Zs at ambient temperature may corrected to Zs at Line maximum permitted operating temperature by dividing by 0.8.
Alternatively maximum Zs for a 20A circuit breaker to BSEN60898 as given in table 41.3 in BS7671 can be corrected to ambient temperature by multiplying by 0.8 (chapter 14 BS7671), this will give you the values of Zs as given in the on site guide.

So long as the Zs for the circuit is less than the tabulated values for a 20A BSEN60898 then the circuit breaker will disconnect in the required time.

View attachment 35140

Thanks Richard this really helped
 

Reply to Can someone help? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Firstly, please go easy as I'm still a trainee! Working on my L3 2365 I'm having trouble understanding the rationale behind adiabatics...
Replies
3
Views
803
Hi, and thank you to anyone who's taking the time to read my question. i'm struggling with the outcome of an adiabatic equation i'm doing and...
Replies
4
Views
3K
Hi everyone I am doing level3 design andI have a circuit to design but I have confusion with radia circuit maximum floor area to understand? I...
Replies
9
Views
6K
Hi guys , hoping someone can help I was due to finish the 2365 course in April this year but with 2 weeks to go some virus came along ( you might...
Replies
3
Views
3K
Can anyone help me clarify the formula in regulation 434.5.2, the time a conductor can withstand a fault current without sustaining damage. t=k2...
Replies
7
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock