Can you feed a consumer unit from another consumer unit, It would be supplied by a non RDC protected MCB. Is this allowed as I have always seen switched fuse disconnection units.
 
I often do it this way for small extensions / kitchen refurbs etc especially when the exisitng board has a nice spare way.
 
Just to add to the above, it is a perfectly good way of feeding a few circuits elsewhere, such as garage, etc.

However, you get poor fault selectivity on MCB feeding MCB. Basically if your final circuit has a PFC that is able to hit the upstream MCB's "instant" magnetic trip point then both MCBs will fire, and so you also loose the other healthy circuits in the sub-CU.

In many cases that is not important enough to worry about, but if it is an issue then your alternative is to spilt the tails and feed the 2nd CU from a switch-fuse (typically in the region of 40-63A).

Also you need to consider RCD protection, ideally in the sub-CU as you suggest, but in turn that means you need cable or routing (i.e. not buried/hidden) that permits no "additional" RCD protection. Usual safe bet is SWA. You might still need upstream RCD protection if you can't disconnect on the sub-main PFC (usually TT earth case) but that can be a 100mA/300mA selectivity (short delay) type that gives your final circuit's RCD protection the chance to act first.
 

Reply to Can you feed a consumer unit from another consumer unit? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Can a domestic consumer unit feed another consumer unit, via the Main Switch. Details are: domestic property with 100A single phase supply...
Replies
9
Views
476
Hi All I'm new here. I have just finished my NVQ and waiting to do my AM2. I have a question on selectivity as it has always slightly confused me...
Replies
5
Views
809
I wondered if it is OK to have 2 x Main Switches in the same consumer unit. One feeding the RCBOs in the House and one feeding the CU in a garage...
Replies
16
Views
851
Client has had a meter installed for a new consumer unit in their shop they are looking to rent out the spare space for a barber shop so they want...
Replies
10
Views
404
Hi. Can a horizontal 200A consumer unit be fitted vertically, or is there a vertical configuration? I have a 350mm wide space...thanks.
Replies
19
Views
838

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock