Looking at a warehouse contract which requires 190M runs of canalis with 31 x 200w lights.

Volt drop is 0.72V per Amp per 100M for 25A 3phase Canalis and 0.3V per Amp per 100M for 40A 3phase canalis.

Am I right in thinking the 40A would be fine? Consultants have said that they want the runs to be split in half due to volt drop, done my own calcs and 40A is fine.

Thoughts/ calcs anyone? Beginning to think I've gone mad?
 

Reply to Canalis calcs in the Lighting Forum area at ElectriciansForums.net

Similar Threads

When I joined this forum a decade or so back, there was a discussion going on about a welder that was connected with a 3-core cable to L1, L2 and...
Replies
3
Views
2K
A question/advice requested re: solar panels (the context is a van/motorhome conversion)... I've got a question re: fusing/breaker for a solar...
Replies
1
Views
2K
Hi, I have just started a new build today, its a large U shaped bungalow with vaulted ceilings etc. I have split the property down into a lot of...
Replies
16
Views
2K
B
Prefix - I've tried to post this in automotive, but it would not let me. This may be because I have not been recently active. Apologies if this is...
Replies
3
Views
3K
W
Hi guys, Looked over some previous posts and done some further reading, and attempted the calcs, just want to check that i am not miles off the...
Replies
8
Views
2K
wade88
W

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock