Testing a touring site for the first time - a.n.other has been doing it for years.
Incoming TNCS to glorified shed in field, outputs to hook ups earthed by SWA sheath, not connected to the big metal dis board, terminated in plastic boxes and connected to a rod so is theoretically TT'ed.
However, the readings I was getting at the hook ups seemed too good to be true, so after disconnecting everything from the rod I measured the resistance between the rod and the earth in the dis board (the TNCS earth). Result was 25 ohms.
As I said, the rod was disconnected from ever thing, so logically the resistance was through the ground.

Is this OK?

Also, elsewhere there is a poor connection in the armour between 2 hook ups, not too bad but notable. Is it worth putting another rod at this point.
 
Testing a touring site for the first time - a.n.other has been doing it for years.
Incoming TNCS to glorified shed in field, outputs to hook ups earthed by SWA sheath, not connected to the big metal dis board, terminated in plastic boxes and connected to a rod so is theoretically TT'ed.
However, the readings I was getting at the hook ups seemed too good to be true, so after disconnecting everything from the rod I measured the resistance between the rod and the earth in the dis board (the TNCS earth). Result was 25 ohms.
As I said, the rod was disconnected from ever thing, so logically the resistance was through the ground.

Is this OK?

Also, elsewhere there is a poor connection in the armour between 2 hook ups, not too bad but notable. Is it worth putting another rod at this point.

I don't understnad what you're saying. Are you saying the TNCS Earth was 25 ohms?

why put a rod in for a poor connection between 2 hook up points? Don't the connections need improving/fixing?
 
I understand that it's a TT earthing system, but I dont understand the scenario described? If the earth between 2 hookups(for example the SWA isn't terminated correctly causing a 'poor connection') why stick a rod in?
 
I understand that it's a TT earthing system, but I dont understand the scenario described? If the earth between 2 hookups(for example the SWA isn't terminated correctly causing a 'poor connection') why stick a rod in?

'cos its corroded badley and I cant get anymore slack on them to make them off properly, ideally it would be easiest to leave that junction alone and sick a rod in.

On part 1 its 25 ohms between the source TT rod and the TNCS earth
 

Reply to Caravan hook ups in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

We have started a business building garden rooms/caravans/mobile homes under the caravan act. We have only done one so far and I got an...
Replies
3
Views
1K
I'm sure this will have been covered before but please bear with me. Have been asked to replace a main Distribution board for a fairly small...
Replies
23
Views
5K
Hi guys I was recently ask by a customer if/how his house could be supplied by his electric car. He wants to charge the car at night on low rate...
Replies
4
Views
1K
Hope this all makes as much sense as i can make of it and my "problem" can get sorted via some guru on here... Just a quick background on myself...
Replies
4
Views
1K
I'm new to this but stuck with an issue, so I'm looking for some help wherever possible. I have just completed a rewire, which I have a potential...
Replies
7
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock