Has anyone got any suggestions ! Been asked to quote a job to supply 6 caravans with power. The supply company is running a supply from the overhead supply to the field.from there it is up to me,not sure what would be best,1 ring main,1 radial or 6 single circuits. the caravans are in a line, the furthest being 60 metres from the pole and a total ring length of 100 metres,the 6 caravans are static,with a design current of 32A per van.any advice ?
 
Some questions first.
1/ The suppliers intake fuse at the pole is what?
2/ Type of earthing?
3/ Is there an isolator?
4/ Does caravan outlet require the full 32A?
5/ What type of cable do you propose to run from the supplier's fuse?
 
Last edited:
I personally would run it in a ring you can get away with a much smaller CSA on the cable

It really is an impossible task to design it over a forum but a few tips can be given

1. Look at a ring main
2 That over head supply is it going to be a TN or TT
3. Have a good look at the regs and section 708 and the restrictions for TNC-S
4 32amp per van is quite a load for a caravan are these holiday or residential.
5. Try and utilize distances perhaps you can feed 2 or 3 vans from on point rather than having 6 separate pints. I do mean points and not sockets as you can utilize 4 sockets to a point.
 
Im sure 16Amp is the norm when i had a look out of intrest at 1. Ringed up in swa from post to post.
As malc said smaller size Swa. 16 Amp blue plug job so you can swap vans with ease -_-
Each post had a Spike(TT)
 
Some questions first.
1/ The suppliers intake fuse at the pole is what?
2/ Type of earthing?
3/ Is there an isolator?
4/ Does caravan outlet require the full 32A?
5/ What type of cable do you propose to run from the supplier's fuse?

thanks for reply
The suppliers intake will be 100A 3-phase,due to another building that will need power in the future
It will be a TT arrangement & cable will be run underground in swa.
 
I thought 32A just to cover it as i`m not sure what appliances the vans are equiped with but 16A would make things easier.Has anyone got ideas on cable size if it was based on 16A Ring
 
a general rule of thumb to calculate the CSA for a ring Main is to multiply the protection device by 0.67 so for instance a 60amp BS 1361 fuse would give you 40.2 amps, so you would use instead of say a 10mm SWA buried for the 60amp supply you would use a 6mm rated at 46amps.

This is a pretty good guide but the main thing is to try and balance it the best you can
 

Reply to Caravan park installation in the Australia area at ElectriciansForums.net

Similar Threads

Need some advice, I have 7 static caravans to connect which need to be connected via TT 1. All the vans have a 30ma RCD main switch internally...
Replies
6
Views
878
Some advise or views would be appreciated. My supply is 100 amp single phase. I purchased my property 3 years ago or so, the owner prior to the...
Replies
29
Views
878
Hi All, I have a client who is developing a plot of land for a single house. Currently, their 100 amp service cut-out is in a cubicle fed by...
Replies
7
Views
1K
Anyone on here with knowledge or experience of wiring for a touring caravan/camping site, whose brains I can pick, please? I may have to design...
Replies
13
Views
2K
So, I already have solar (an older FITS installation) and it's been particularly successful so I want to extend this. I'd like to do two things at...
Replies
1
Views
556

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock