A caravan site I have recently worked on had a switch room adjoining a sub station, in the switch room the circuits feeding a large site are terminated in 8 x 200 amp three phase and neutral Glasgow switch fuses, these are marked in pairs as rings going east, west, south and north. My job was to isolate cables from a toilet block and reconnect them in a fibreglass cabinet as the toilet block was to be demolished, further investigation found that this was part of the north ring which fed 3 other buildings and at the switch room was fed by 2 switch fuses one on each outgoing cable (95mm aluminium)however the ring was broken in one of the buildings isolated at 1 of 2 switch fuses which both fed onto a bus bar .In the toilet block was an mccb panel board feeding sub mains to (areas of caravan pitches) which also had to be moved this was fed by 2 cables onto separate mccbs as part of the ring.
After a rush to get the cables moved as demolition had already begun, it came to testing, I asked the maintenance electrician how they had previously been tested and could I see the test sheets as I could see a few issues.
Namely 200amp three phase on 95mm aluminium cable and loop impedance's which would be to high for operation of either the 200 amp cartridge fuses or the mccbs in the panel board as depending on where the ring is separated could give an EFLI reading of between 0.2 and 0.4 ohms which is to high for both.
His answer was that they were tested with the ring made so I explained this meant he was feeding via 2 X 200 amp fuses in 2 separate switch fuses, not good and all other options require rehashing the mains and the introduction of rcd protection which he doesn't want.
Has anyone else come across such a system which was wired by the local electricity authority as was in the day and any ideas what to do about it.
After a rush to get the cables moved as demolition had already begun, it came to testing, I asked the maintenance electrician how they had previously been tested and could I see the test sheets as I could see a few issues.
Namely 200amp three phase on 95mm aluminium cable and loop impedance's which would be to high for operation of either the 200 amp cartridge fuses or the mccbs in the panel board as depending on where the ring is separated could give an EFLI reading of between 0.2 and 0.4 ohms which is to high for both.
His answer was that they were tested with the ring made so I explained this meant he was feeding via 2 X 200 amp fuses in 2 separate switch fuses, not good and all other options require rehashing the mains and the introduction of rcd protection which he doesn't want.
Has anyone else come across such a system which was wired by the local electricity authority as was in the day and any ideas what to do about it.