I am carrying out a refurbishment job on this old panel board and fitting in a new panel board from Schneider. The current supply to this building is a 100amps BS88-2 Gg (assuming). I am planning to protect the outgoing submains with the NSX100 ML 2.2 set at 100 and 63 respectively. I don't know the full load but the current submains have 100Amps MCCBs and 63Amps. For some reason the Schneider quick selectivity tool says there is no selectivity between the upstream 100amps fuse and ML 2.2 but shouldn't it be fine? Here is the picture : ML 2.2 @100 and BS88-2 Fuse.
1615235948648.png

ML2.2 @63 and BS88-2

1615236012927.png
Looking at this graphs, the protection device for the submains would trip first before the main fuse.

Any help would be appreciated, thank you.
 
It depends on the fault level, sure at low currents up to circ 800A there is coordination, and most likely discrimination, however once you get into the current limiting phase of the fuse operation the I^2 t let-through of the mcb/mccb will be more than the pre-arcing I^2 t operation of the fuse.

To check, you need further curves/tables the I^2t pre-arc will be easy to find, but the let-through on a mcb/mccb is usually harder to find for some reason.
 
It depends on the fault level, sure at low currents up to circ 800A there is coordination, and most likely discrimination, however once you get into the current limiting phase of the fuse operation the I^2 t let-through of the mcb/mccb will be more than the pre-arcing I^2 t operation of the fuse.

To check, you need further curves/tables the I^2t pre-arc will be easy to find, but the let-through on a mcb/mccb is usually harder to find for some reason.
Sorry for the delay in reply but thank you Julie. I will investigate this further.
 
The Schneider on-line tool has combinations where it gives no selectivity results and times when it does, based on combinations of stuff but with no obvious reason why.

As @Julie. says for the plots you have to realise the fuse continues down from 0.1s smoothly but gradually reaching the constant-I2t region with a slope of 2 decades time per decade current on the log-log scale.

The two regions (extrapolated fuse & breaker) cross at around 0.8kA so you have overload selectivity but no practical fault selectivity. Unfortunately that is generally the case with OCPD close in ratings of any types (except fuse-fuse at ratios of 1.6 or more where you generally get total selectivity).

But I am struggling to understand what you have as a 100A supply fuse and multiple sub-mains off that with 100A and 63A MCCB does not appear to ever had much chance of providing selectivity!
 
Also what sort of loads do you have?

In the example config for the Schneider MCCBs you show above the "instant" trip is at about 140A / 90A. That is similar to a 50A/32A B-curve MCB, or 32A/20A C-curve MCB so any high inrush load like a medium DOL-started motor, etc, that might trip that sort of MCB would al;so be able to take out the sub-main feed!
 
The Schneider on-line tool has combinations where it gives no selectivity results and times when it does, based on combinations of stuff but with no obvious reason why.

As @Julie. says for the plots you have to realise the fuse continues down from 0.1s smoothly but gradually reaching the constant-I2t region with a slope of 2 decades time per decade current on the log-log scale.

The two regions (extrapolated fuse & breaker) cross at around 0.8kA so you have overload selectivity but no practical fault selectivity. Unfortunately that is generally the case with OCPD close in ratings of any types (except fuse-fuse at ratios of 1.6 or more where you generally get total selectivity).

But I am struggling to understand what you have as a 100A supply fuse and multiple sub-mains off that with 100A and 63A MCCB does not appear to ever had much chance of providing selectivity!
It is an old school and looks like things were added on over the years, so I don't think they cared about selectivity that much as long as the final circuits tripped.
 
Also what sort of loads do you have?

In the example config for the Schneider MCCBs you show above the "instant" trip is at about 140A / 90A. That is similar to a 50A/32A B-curve MCB, or 32A/20A C-curve MCB so any high inrush load like a medium DOL-started motor, etc, that might trip that sort of MCB would al;so be able to take out the sub-main feed!
Yes, that's another problem. I don't know the loads but the highest breakers they have are 32Amps type B. I guess this problem can be worked around by using 160 MCCB ML 4.2 or higher and setting the tripping point (ir) at 100 and then setting the instantaneous tripping at 200A. I guess full selectivity won't be obtained but as long as the submains are adequately protected, and discrimination between final circuits and the submain protective device is there, it should be okay.

Any other suggestion on how to get around this would be appreciated.

Thanks.
 
Yes, that's another problem. I don't know the loads but the highest breakers they have are 32Amps type B. I guess this problem can be worked around by using 160 MCCB ML 4.2 or higher and setting the tripping point (ir) at 100 and then setting the instantaneous tripping at 200A. I guess full selectivity won't be obtained but as long as the submains are adequately protected, and discrimination between final circuits and the submain protective device is there, it should be okay.

Any other suggestion on how to get around this would be appreciated.
How many sub-mains, are they single or 3-phase, and what loads do they actually need?

It might seem very old-school (pun intended!) but how about a busbar chamber and a couple of 63A fused-switches for each sub-main?

They would have total selectivity with the 100A incoming fuse, and moderate selectivity with final circuit MCB/RCBOs.

I recently looked at that for another question and, at least for the Hager one I had a table of selectivity values for, the 63A fuse feeding 32A B-curve RCBO was OK to 1.5kA faults on the final circuit which could well be above what you see at the end of the sub-main and wiring to appliances, etc.
 
This was the post:
 
The electronic MCCB are not cheap, so you might find that a couple of decent fused-switches such as Schneider SQB0633K, or maybe better the 100A SQB1003K with 63A fuses fitted so upgrading is possible in the future, will work out about the same cost.

Of course replacing those fuses is a job for an electrician, not like re-closing a MCCB, but ideally they won't be blowing unless you have a serious fault anyway!
 

Reply to Carrying out a refurb on old panel boards, worried about discrimination. in the Electricians' Talk area at ElectriciansForums.net

Similar Threads

Hi everyone Ive just had an electrical condition report conducted on a mixed-use property, and I am extremely surprised that after the last report...
Replies
11
Views
2K
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K
Hi Guys A first floor flat I rent out requires an EICR. It was purpose built in 1990. I'm no longer in business or up to date with regs and...
Replies
10
Views
761
Currently quoting for a job that needs to be done next week and working out how best to proceed, so thoughts welcome. Current situation: -->PME...
Replies
6
Views
4K
Hi Guys, Been asked to look at an old rambling pub/restaurant/ hotel by the new tenants. 8 letting bedrooms, bar / restaurant area, couple of...
Replies
10
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock