If it really has to be a MCCB board then you are probably as well giving up on the idea of selectivity on the sub-main to incoming fuses, and just got for the basic model rather than trying to fiddle with the fancy electronic settings to try and walk the line between the MCCB/fuse on the supply side and the MCB/MCCB on the sub-DB side.
 
If it really has to be a MCCB board then you are probably as well giving up on the idea of selectivity on the sub-main to incoming fuses, and just got for the basic model rather than trying to fiddle with the fancy electronic settings to try and walk the line between the MCCB/fuse on the supply side and the MCB/MCCB on the sub-DB side.
Thank you for suggestions and the links, I will have a look through them.

There are 6 single phase submains and 2 three phases - submain. Unfortunately I don't know the exact loads at this time.

The bus bar chamber idea sounds good but they want an upgrade to 6 way MCCB panel board. Like you said the fuses probably won't blow but circuit breakers are easily switched on. The MCCB will be more expensive but the school will have to swallow it.
 
You might want to check the main fuse, as that is quite a lot of sub-mains coming off 3*100A for example, so if they turn out to be 160A or more then you have an easier job.

I had a go at the Schneider on-line tool but it seems broken for me today :(

I would concentrate on getting tolerable MCB/MCCB selectivity using the short-delay aspect of the fancy MCCB, that way in most cases the selectivity falls back to incoming fuse and final MCB, and that is probably no problem.

Yes, a sub-main fault might not open the MCCB before the incoming fuse, but that is a lot less likely than some final circuit/appliance giving them grief.

If you can find out loads and the PFC & PSCC at each DB just now it would help to decide how well the whole system would work.
 
You might want to check the main fuse, as that is quite a lot of sub-mains coming off 3*100A for example, so if they turn out to be 160A or more then you have an easier job.

I had a go at the Schneider on-line tool but it seems broken for me today :(

I would concentrate on getting tolerable MCB/MCCB selectivity using the short-delay aspect of the fancy MCCB, that way in most cases the selectivity falls back to incoming fuse and final MCB, and that is probably no problem.

Yes, a sub-main fault might not open the MCCB before the incoming fuse, but that is a lot less likely than some final circuit/appliance giving them grief.

If you can find out loads and the PFC & PSCC at each DB just now it would help to decide how well the whole system would work.
Yeah, that's a good point. I will get the main fuse confirmed.

I might be able to get the loads confirmed as well.

Thanks.
 

Reply to Carrying out a refurb on old panel boards, worried about discrimination. in the Electricians' Talk area at ElectriciansForums.net

Similar Threads

Hi everyone Ive just had an electrical condition report conducted on a mixed-use property, and I am extremely surprised that after the last report...
Replies
11
Views
2K
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K
Hi Guys A first floor flat I rent out requires an EICR. It was purpose built in 1990. I'm no longer in business or up to date with regs and...
Replies
10
Views
760
Currently quoting for a job that needs to be done next week and working out how best to proceed, so thoughts welcome. Current situation: -->PME...
Replies
6
Views
4K
Hi Guys, Been asked to look at an old rambling pub/restaurant/ hotel by the new tenants. 8 letting bedrooms, bar / restaurant area, couple of...
Replies
10
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock