Discuss Caught out by mt own lazyness..... in the UK Electrical Forum area at ElectriciansForums.net

Doomed

-
Esteemed
Arms
Reaction score
685
Did an EICR of a rented property, 2 up 2 down, old, one lighting circuit, cooker, ring and 2 radials (2 sockets in kitchenon one, hall socket on other).
All readings not to bad, not perfect I/R on kitchen radial, but damp walls so I wasn't surprised, end of line readings all good, realised that there must be loads of hidden joints on the lighting, so took readings at the furthest grond floor point and both ends of first floor.
Bonding up to date, but no RCD protection.
As rented recommended fitting RCD protection, gave landlord options and she went for a shiney new distribution board.
Came back, fitted it, retested all socket and cooker circuits and then got lazy..... as only the one lighting circuit checked the ground floor point I tested at last time as that had the highest reading last time and thoght jolly good, home time.
Silly me.
Two hours later called back when the tenant got home and tried to put the lights on upstairs - RCD trip!
After lots of hunting found a JB with the neutral and earth linked - AH HA I thought... - nope, take it out and no lights - upstairs missing the neutral - great, lifting boards and running a new feed 8pm at night with a moody tenant on my back.
Serves me right.
:(
 
Didnt you IR on eicr?
Yes, at the fuseboard, and that showed no issues as the neutral was not connected to the point where the earth link was - I would of only of found it if I I/R was done at the upstairs lights, which means I would be I/R ing at every light fitting during a test to find that sort of thing.
 
Yes, at the fuseboard, and that showed no issues as the neutral was not connected to the point where the earth link was - I would of only of found it if I I/R was done at the upstairs lights, which means I would be I/R ing at every light fitting during a test to find that sort of thing.
Surely the ir test would show neutral and earth Linked if tested at board.
It wouldn't have made any difference where you tested it. If the neutral and Earth are linked anywhere on the circuit it would of shown on testing at the board.
 
As I said the neutral was broken prior to the join, therefore it did not show up, someone put the join in to use the earth as a neutral!
 
As I said the neutral was broken prior to the join, therefore it did not show up, someone put the join in to use the earth as a neutral!
But the earth must have been continuous back to the board so you would have got a reading L-E through lamps, or did you remove all lamps?....In which case why when a LN-E test is the way to go on an EICR?
 
Not if the light switches were not switched on when tested. Or the lamps removed.
There was a break in the neutral, the neutral was connected to earth on the load side of the break, therefore, the earth and neutral become a combined conductor back to the PME terminal.
 
Like your drawing Anthony brag. Makes perfect sense, but...

In post one no mention of break in neutral. Just neutral and Earth connected.

In post 4 a bit more confusing, it says neutral was not connected where earth was linked. Not sure how to interpret that one.

Maybe wording not ideal.

Question to doomed, has anthonybrag got it right in his drawing. If so case cracked.
 
Like your drawing Anthony brag. Makes perfect sense, but...

In post one no mention of break in neutral. Just neutral and Earth connected.

In post 4 a bit more confusing, it says neutral was not connected where earth was linked. Not sure how to interpret that one.

Maybe wording not ideal.

Question to doomed, has anthonybragg got it right in his drawing. If so case cracked.
See post 7
 
Thanks for the drawing Anthony made things much clearer,I know I’m missing something here but why would the rcd only trip once the upstairs lights were switched?
When any switch is in the on position there would be Current through the residual current devices live, but no return feed through neutral as the return path would be via the cpc. I balance trip.

If all lights switched off no current through live and no current through neutral. Also non of the lights neutrals are actually connected to the neutral bar in the earth. No imbalance no trip.
 
Thanks Pete that makes sense, What’s confusing me is it only tripped with the upstairs lights when there is only a single lighting circuit? Not doubting anyone here just trying to keep up ha ha :)
 

Reply to Caught out by mt own lazyness..... in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Good day. First time poster. We recently had an electrician perform the EICR, as this is a newly purchased property I thought'd I would have the...
Replies
7
Views
710
Hi all, Gone to look at a intermittent ground floor sockets fault today, the RCBO was tripping at random times with no pattern. Nailed down a...
Replies
11
Views
1K
An RCD keeps tripping. Please see attached photo of the board (2 photos attached). I’ll call the breakers: MCB (1) marked ‘Upstairs lighting’...
Replies
4
Views
1K
I have an issue with a home lighting circuit 6A RCBO provides power to 13 bulbs which randomly keeps tripping, when I say randomly it keeps...
Replies
8
Views
3K
Hello All, I have just found out that a family member who is having some Building work done has been advised to insulate above the Kitchen...
Replies
16
Views
813

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock