Discuss CCC 1.5mm T&E ref method B? in the UK Electrical Forum area at ElectriciansForums.net

happysteve

-
Esteemed
Arms
Supporter
Reaction score
2,120
Morning! Would someone please mind checking the big brown book for 1.5mm flat sheathed cable, ref method B, CCC? Page 456 from memory. Only have the blue book in the van, which lists refs A and C but not B.

Voltage drop is ok, as is Zs.

Thanks! :)
 
Surely clipped direct is in all regs books ? clipped direct is the most common one most sparks use when doing calcs
 
Surely clipped direct is in all regs books ? clipped direct is the most common one most sparks use when doing calcs
Yes, ref C, clipped direct, is in the book and alwsys has been.

Asking about ref B, which is enclosed, where conduit is not in insulation.

Historically, they only listed A, C, 100-103. In the brown book, they started listing B as well
 
1.5mm flat sheathed cable, ref method B: CCC is 16.5A

(yep, page 456!)
Thanks @tims22 much appreciated :)

The existing cable that I assumed was 2.5mm T&E when I quoted for the job turned out to be 1.5mm 3C&E, with a core unused. Protected by a B16. I had a feeling it would be close.
 
Lots of sparks seem to turn their nose up to 1.5 on a 16a, but in reality its perfectly fine more often than not
 
Lots of sparks seem to turn their nose up to 1.5 on a 16a, but in reality its perfectly fine more often than not
It’s just that they are used to using it with 6 or 10A breakers for lighting
when you do it all the time, it becomes the norm and anything outside of the norm is assumed to be bad.
 

Reply to CCC 1.5mm T&E ref method B? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have had my kitchen rewired and plastered. I have had a 6mm t+e on a dedicated 32a circuit for a 60cm electric cooker. In hindsight, had i known...
Replies
11
Views
681
I have a question,about cable loadings, just to satisfy my own curiousity. The background detail is a bit long, apologies. If you get bored...
Replies
1
Views
1K
could anyone take a look at these figures please and tell me if they are ok or not. thanks in advance watts where stated 60w x 3 60w x 3 Ib...
Replies
8
Views
1K
Still revising for the 18th on Friday and have become stuck not being able to find the reference to the following in the BBB. I know where the...
Replies
6
Views
1K
  • Article
Merry Christmas from ElectriciansForums.net What a weird year we’ve had! We will need to keep our wits about us during these next couple of...
Replies
23
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock