Discuss Ceiling heating in the Electric Underfloor Heating Wiring area at ElectriciansForums.net

Reaction score
1
Hi all my ceiling heating stopped working recently and I want it back on for the winter. I have checked the feed to the contactor which was live but was the voltage was not going through the contactor. I replaced the contactor with a similar 4 pole model but have the same issue. I have wired it exactly as the previous one. Any ideas on what the problem could be? I have some electrical experience
 
TL;DR
New contactor doesn’t work
sounds like your contactor is not receiving it's coil supply. try pressing the manual contactor button.if it works the, trasce the coil signal back. could be a faulty stat. ofr something else.
 
stat or timeclock are the most likely culprits
 
Presumably you mean in just one room/location, not the whole flat/house?
Has anyone disturbed the ceiling, put up new light fittings or worse, recessed lights? Although if the contactor is not closing the fault lies before that and likely to be the thermostat as others have said.
 
Just re-read again,
You have a switched live supply at the contactor so thermostat is working! Brand new coil (correct voltage?) Perhaps lost Neutral to complete the circuit?
 
The only ceiling heating I have seen, is 20A radial to each room with its own thermostat per room.
Do you only have 1 stat to control the whole set up.?
 
The only ceiling heating I have seen, is 20A radial to each room with its own thermostat per room.
Do you only have 1 stat to control the whole set up.?
Same as me, I’ve seen in only one estate in Woodford green, used as a prototype, realised it was a crap idea and doesn’t work unless your 6 foot 9 and binned it in favour of storage heaters(not much of an improvement lol)

most of the flats have ripped it out now and have plug in heaters everywhere
 

Reply to Ceiling heating in the Electric Underfloor Heating Wiring area at ElectriciansForums.net

Similar Threads

I'm after some advice please, I have carbon mat underfloor heating throughout my bungalow, each room has its own thermostat and are fed via a...
Replies
1
Views
791
m having a bit of an issue that is proving difficult to resolve. For 2 years I have been having no problems with my setup. I have a 3 zone house...
Replies
1
Views
1K
Just replacing a ceiling light and could do with some guidance on sorting out all the wiring. This is how it was: And the light is expecting...
Replies
1
Views
800
I've pretty much sussed out the wiring for the radiators and underfloor heating, thanks to help from the forum. I do have one more question...
Replies
6
Views
665
Hi guys, I have recently encountered that my circuit breaker for the upstairs lights keeps tripping. I flick it back on and immediately it trips...
Replies
7
Views
876

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock