can I had, if another gas engineer turns up ,boy he would not like that having two sauces of power ,either rip out and start again and sod the tiles or work under Neath the flooring .e.g. plaster board if possible .
 
Just to add something else [And haven't wired a Y plan for ages so could be wrong], but don't you also need a switched 'HW off' core from the programmer on a Y plan too ? If so that would be six cores in total.:rolleyes:
 
Just to add something else [And haven't wired a Y plan for ages so could be wrong], but don't you also need a switched 'HW off' core from the programmer on a Y plan too ? If so that would be six cores in total.:rolleyes:
I read it as the OP needed 5 cores to the boiler not the programmer. If it is the case that you describe then he could install a relay. Use HW on to energise the coil and wire the grey of the mid position valve and normally open of the cylinder thermostat to normally closed of the relay.
 
I read it as the OP needed 5 cores to the boiler not the programmer. If it is the case that you describe then he could install a relay. Use HW on to energise the coil and wire the grey of the mid position valve and normally open of the cylinder thermostat to normally closed of the relay.

I probably misunderstood Lee, it's that time of day when my old brain has had enough. :D
 
If the boiler needs only sw live,N and earth and the programmer is a two-channel stand-alone programmer then could have the existing supply have the programmer there and put an isolator before the boiler.
 

Reply to Central heating programmer cable 3 and earth in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have a fully pumped Y plan heating system using a Potterton EP2 programmer. Drayton MA1 Diverter valve. I have just replaced the Actuator head...
Replies
4
Views
632
I have a Firebird oil boiler that is controlled by a Honeywell timer (no thermostat) that has channels for hot water and central heating...
Replies
8
Views
448
I have not had to do the wiring for a wet underfloor heating system before. I think I started a thread fairly recently and had some very good...
Replies
24
Views
2K
Electrician has done rewire, plumber with not much space has some central heating and hot water pipes touching in some places. See images...
Replies
4
Views
2K
Hi all, Hope you're keeping well I'm currently wiring a small commercial premises. 3 phas incoming supply, 16sq cables As it is in an urban...
Replies
3
Views
331

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock