Discuss Certificate Building Control in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
7
Hi all, I am a home owner and our builder has completed a garage conversion with the electrician installing a new 4 way distribution board. The electrician has now gone completely silent, does not answer phone, email, text and appears to have left his address. We need a certificate for building control, so we need another electrician to provide this. How much would this cost? We are in the SL6 postcode area.
Regards
 
As westward said, only the electrician who installed it can provide an installation certificate and a building control notification certificate.
If this is not possible, then you can ask the building control officer if they will accept an EICR (electrical installation condition report), which you will have to pay an electrician to complete.
Prices for this vary depending on location.

On the other hand, if the builder engaged the electrician, your contract is with the builder, not the electrician. If so there may a case for insisting the builder have an EICR done at his expense. (Good luck with that though)
 
It may be in the builders best interest to ensure you get it as BC shouldn't sign off the whole project without all the necessary paper work in place. (Unless of course the electrics are the only element requiring BC notification)!
 
Hi all, I fully understand trying to cost this without an inspection is tricky but I need a rough price so the solicitor can put that in the legal documentation. Also if I posted this person’s name and company details would someone be able to assist me in contacting him - they are in the High Wycombe area post code HP15.
 
That is impossible to say through an internet forum. Depends on the standard of work and whether any issues are found and need rectified, if any.
Hi MJPD29, I fully appreciated your reluctance in this matter but can I propose a scenario:
One of the electricians you work with and trust is unable to provide the installation for a job. You implicitly trust them; so what would you charge to inspect and provide the electrical certificate.
I do fully appreciate your reluctance here but any input would be welcomed!
 
That is impossible to say through an internet forum. Depends on the standard of work and whether any issues are found and need rectified, if any.
Hi MJPD29, I fully appreciated your reluctance in this matter but can I propose a scenario:
One of the electricians you work with and trust is unable to provide the installation certificate for a job. You implicitly trust them; so what would you charge to inspect and provide the electrical certificate.
I do fully appreciate your reluctance here but any input would be welcomed!
 
Hi all, I fully understand trying to cost this without an inspection is tricky but I need a rough price so the solicitor can put that in the legal documentation.
It might help understand why another electrician would not want to complete an EIC for work done by another, even if he trusted him, if you read what the signatory is declaring on the form:
That is why it was suggested, if the Building Inspector would accept an EICR, that would be a more pragmatic way of resolving the issue.
IMG_0432.jpeg
 
This issue appears to pop up every now and then m where by the orginal sparks either disappears mid job or near the end of the job and doesn't leave any paper work or certs.
I have done EICRs for a couple customers in the past who have had rogue sparks quit near the end of the job, My building control in my area have never had any issue with this.
As for the price , I am £95 per hour if that helps the OP gauge the cost
 
I propose a scenario:
One of the electricians you work with and trust is unable to provide the installation certificate for a job. You implicitly trust them; so what would you charge to inspect and provide the electrical certificate.
No ‘bona fide’ electrician will sign of others work, no matter how much you trust them, #13.
They will however do an EICR on the work in this case a garage conversion which can then be submitted to building control who if happy with the EICR will issue a building regulation Part P certificate.
Sticking my neck out, and as you don’t mention any details of the installation, supply, earthing, number of circuits etc (and you only wanted a rough price) …. £550 plus vat.
 
As the others have said, no one apart from the electrician who carried out the work can issue you with an Electrical Installation Certificate (EIC).

The only thing you can do now (assuming you continue to be unable to contact the electrician), is to get a different electrician to carry out an Electrical Installation Condition Report (EICR) on all of the new work. The results of this report will come back as satisfactory or unsatisfactory.

The building inspector is 'likely' to accept a satisfactory EICR rather than the required EIC, but it is not a fore gone conclusion and it would be best to check with them first.

I can tell from your posts you just want a figure. A rough idea of the cost for carrying out the report would be £200. You would then need to pay further costs if the report was unsatisfactory. It is impossible to say how much this would cost. Anywhere from £80 for a faulty socket, to £5000 to completely redo all the electrics. Obviously these are silly figures and just to show that it is again impossible to give a figure for any remedial work that may be required.
 
It might help understand why another electrician would not want to complete an EIC for work done by another, even if he trusted him, if you read what the signatory is declaring on the form:
That is why it was suggested, if the Building Inspector would accept an EICR, that would be a more pragmatic way of resolving the issue.
View attachment 112681
Hi Avo Mk8,
I am in no shape or form an electrician and I do truly appreciate all of the kind advice this forum and its contributors have provided. I’ll raise this with my builder, who is probably aware of this EICR route, and I’m sure we can reach a pragmatic solution.
Again thanks for all for the assistance, it is appreciated.
 
Hi MJPD29, I fully appreciated your reluctance in this matter but can I propose a scenario:
One of the electricians you work with and trust is unable to provide the installation certificate for a job. You implicitly trust them; so what would you charge to inspect and provide the electrical certificate.
I do fully appreciate your reluctance here but any input would be welcomed!
A rough figure would be 250 for an EICR, any further work to be carried out would then be charged on top of that.
 
The electrical work mentioned is a garage conversion with a 4-way board, and the EICR only needs to cover those 4 circuits (or less, if not all used) plus earthing & bonding, there should be no need to check the rest of the house (though it might be a good idea to do so, depending when or if ever done). The extent & limitations will define this.

Depending exactly what is converted (single garage, double garage) and to what (one room with a light and a few sockets, or something more?), the EICR cost might not be as high as some of the suggestions. Obviously any remedial work depends on the findings.

It might be worth posting a photo of said 4-way consumer unit, sometimes you can tell a lot about the quality of the install from that!
 

Reply to Certificate Building Control in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

As per Part P of Building Regs, once electrical work is performed by a registered competent person, the installation certificate needs to be given...
Replies
21
Views
3K
Hi Everyone, I had a new consumer unit installed in December 2021, the electrician said that he had more testing to complete and would come back...
Replies
28
Views
3K
Hello, I understand that from the 15th of June testing and commissioning of vents and fans is now compulsory and that also since last year any...
Replies
47
Views
4K
Had a lovely conversation/argument with building control this morning, the scenario is this, Completed job (4 flat rewire) EIC’s sent to client as...
Replies
12
Views
3K
This is a strange one, my neighbour is a bit mad, he had a largish extension built in about 2015, the builder attempted to do everything including...
Replies
3
Views
957

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock