Discuss Checking for breaks On A Long Cable in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Once you test and determine there is a break,the fun can then start, using your meter to measure resistances calculate exactly where along its length that break has occurred
 
Simply check continuity,on each conductor,until you find O/C....then,pull the copper inner conductor,out of the insulation.
Then,measure the length of that copper,and note it down.
Measure the total length of the cable,deduct the length of the copper,and then measure that distance,from the other end.

....This,is where your break is. ;)
 
Simply check continuity,on each conductor,until you find O/C....then,pull the copper inner conductor,out of the insulation.
Then,measure the length of that copper,and note it down.
Measure the total length of the cable,deduct the length of the copper,and then measure that distance,from the other end.

....This,is where your break is. ;)
then when he's cut the cable at the break, re-insert the copper conductor he's pulled out, and repair. :D:D:D.
 

Reply to Checking for breaks On A Long Cable in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi guys, Had an issue at a recent survey where doing a quick check and found we had pme with a reading of 0.44 ohms. Called the network and they...
Replies
5
Views
367
Hi, thanks for reading this. Ive been asked to look at a job where the DNO connection (single phase 80A TT) is a long run to the final circuits...
Replies
4
Views
280
Some advise or views would be appreciated. My supply is 100 amp single phase. I purchased my property 3 years ago or so, the owner prior to the...
Replies
29
Views
854
Hi! DIYer here. I have an MCB running to a cooker isolator switch. The RCD connected to this set of MCBs is tripping and isolating the cooker MCB...
Replies
4
Views
759
I had an interesting little job this morning. Three sockets in an extension were not working and haven't worked for quite some time (years). It...
Replies
0
Views
274

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock