Discuss Chilton 60A 770mA Current Operated ELCB in the UK Electrical Forum area at ElectriciansForums.net

hawk84

-
Reaction score
0
Came across this recently doing an EICR.
Just wondering if anyone has any information on this.
Its a Chilton 60A Current operated ELCB
Voltage Rating 415
Current Rating 60A
Rated Tripping Current 770mA
Catalogue No. CEHB3060/C

I'm curious about the 770mA Rated Tripping Current.
There are some photos that may help.
20170801_143425.jpg
20170801_143449.jpg
 
Difficult question Mate I have been on google trying to find ananswer and all I get is the operation of a Voltage ELCB when I try Current ELCB all I get is now known as RCDs. Maybe best to wait for Lucien to appear he would probably have the answer. Lucien is the Forms go to guy on all things out of the ordinary.
 
'Ello Pete!

For practical purposes it's an RCD by another name. Historically, ELCB implied voltage-operated simply because that was what was being made when the term was introduced. When they started making 'modern' differential current-operated types, before the term 'residual current' was standard, they referred to them as current-operated ELCBs.

It's got the same bits as a modern one, just bigger. The breaker and its tripping mechanism may in fact be the same as used in some VOELCBs, just with the addition of the balance transformer and what seems to be a rather elaborate test arrangement, with an auxiliary transformer behind that board near the test button.

As for the 770mA tripping current, I can't think what that derives from. For a touch voltage of 50V that would require Zs < 65Ω, which doesn't ring any bells with me. What is it protecting? It looks like it's inside a machine panel, with those numbered cables in the Redspot fuseholders. What is the earthing system of the installation?
 
'Ello Pete!

For practical purposes it's an RCD by another name. Historically, ELCB implied voltage-operated simply because that was what was being made when the term was introduced. When they started making 'modern' differential current-operated types, before the term 'residual current' was standard, they referred to them as current-operated ELCBs.

It's got the same bits as a modern one, just bigger. The breaker and its tripping mechanism may in fact be the same as used in some VOELCBs, just with the addition of the balance transformer and what seems to be a rather elaborate test arrangement, with an auxiliary transformer behind that board near the test button.

As for the 770mA tripping current, I can't think what that derives from. For a touch voltage of 50V that would require Zs < 65Ω, which doesn't ring any bells with me. What is it protecting? It looks like it's inside a machine panel, with those numbered cables in the Redspot fuseholders. What is the earthing system of the installation?
Thanks Lucien knew you would be able to come up with the goods, hope the OP appreciates your efforts.
 
Hi, thanks for the quick response.
It's the front end RCD on a T.T. Installation. The installation is a water pumping station, and the RCD is mounted within the MCC panel. It just seemed odd to me the 770mA rating. It's as if it's given the rating after on site commission and testing, as the details are hand written. I have more tests to carry out on the site, and will probably be doing some remedial/upgrade works as this is the only RCD on the installation.
 

Reply to Chilton 60A 770mA Current Operated ELCB in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

BEFORE I pull my hair out looking over a gazillion google results..... wondered if anyone here has come across a device that will do something...
Replies
1
Views
863
Hi all, Just to be clear, I'm not looking for advice on upgrading but rather just clarification of our existing setup. We need to upgrade the...
Replies
12
Views
1K
Hi everyone :) my first post here. Quick background I'm a newly qualified installer of somewhat advanced years whose just starting out in the...
Replies
12
Views
1K
Hi friendly people, As you may be aware, I'm a plumber, so quite possibly what I am seeing is correct, though it seems a bit odd to my untrained...
Replies
4
Views
5K
Over the last few days, I have stumbled across a number of threads that seem to point to a prevalent misunderstanding. Either that, or I have been...
Replies
6
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock