Hi

I’ve got a set of filament lamp Christmas lights, which I think is quite old.

It is a set of 80 lights, and the lamps are rated at 2.4V, 0.29W, 120mA.

The transformer is rated 24V(AC), 0.7A, 16.8VA.

It had 8 ballast lamps installed, so I assume 1 ballast lamp for a string of 9 normal lamps. However I don’t really like how the strings of 9 lamps flash on and off randomly, so I have replaced all the ballast lamps with normal lamps of the same rating as the others.

However, I thought this might overload the transformer because 80 x 0.29W = 23.2W, which is more than the rating of the transformer- 16.8VA( which I think is the same as 16.8W??).
So my question is: will this overload the transformer?

If so, would it be ok to only put in 55 lamps, to give a wattage of 15.95W, which is under the VA rating of the transformer?

Thanks for any replies!

image.jpg


image.jpg


image.jpg
 
But, the OP is correct. VA and Watts are the same as far as filament lamps are concerned. Having all the lamps on continuously will overload / overheat the transformer, but leaving a lamp out of some strings so that the total load is less than 17W will be OK.

I've always marvelled at how for over half a century, it was customary to celebrate winter festivals, especially Christmas. by connecting lots of small filament lamps in series, instead of the usual parallel. If they had used series-connected lighting in Judea around 4BC, you could understand wanting to keep that tradition, but there's very little surviving information on Roman electrification schemes.
 
Still seems a bit of a bodge for me. And those type of filament bulbs were never very reliable. I'd go for a nice new LED set.
 
It’s part of the Christmas tradition:- getting the old string of lights out the box, plugging them in and going along the string looking for the broken bulb/ lamp.

1984... a couple of years before leaving school I decided to rewire the family’s static tree lights by adding a 12v spotlight relay from Halfords, a flasher unit from a roadworks amber light and a few batteries to power the flasher.
So flashing tree lights before they were so popular, and quite effective, although a rather loud click sound every second or so
 
Non contact volt sticks are good for finding duff bulbs/lamps in old style strings.
 

Reply to Christmas lights transformer rating in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Im new to the forum and wanted to check something and maybe get some advice confirmation. Ive got halogen wall lights which use a...
Replies
6
Views
1K
I have halogen lights in my kitchen under the wall units, there are ten lights altogether bulbs are either 10 watt or 20 watt G4 bulbs ( not sure...
Replies
1
Views
753
I am looking at installation of an architectural dimmer, that is will supply 6 channels, with 20A circuits each (2400W ea). Our hall has can light...
Replies
2
Views
705
Good evening I’m still learning at college and curious as Xmas just approaching regarding Xmas led string lights and there power supply...
Replies
0
Views
918
Hello I have recently moved home and I looking to upgrade lighting across the house to LED. In the kitchen I have found that there is installed...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock