Discuss Circuit breaker keeps tripping in the DIY Electrical Advice area at ElectriciansForums.net

Reaction score
0
15 amp Eaton breaker controls office and 3 hallway lights. 9 year old house. 200 amp panel.. Wind storm last week, breaker tripped. Re set it on, but it keeps tripping. Figured it was toast, so ordered a couple new breakers. (None in stock locally). Pulled an identical breaker from the panel and wired it in. It also tripped off, with a little spark. Any thoughts?
 
15 amp Eaton breaker controls office and 3 hallway lights. 9 year old house. 200 amp panel.. Wind storm last week, breaker tripped. Re set it on, but it keeps tripping. Figured it was toast, so ordered a couple new breakers. (None in stock locally). Pulled an identical breaker from the panel and wired it in. It also tripped off, with a little spark. Any thoughts?

Something is causing a short or an overload. Needs some testing to be done on that circuit.

Any outside lighting etc. which may have got damaged or waterlogged in the storm?
 
It's interesting that you should ask about outside lighting being damaged. Right after the storm, I found an outside GFCI completely melted. The inside switch that controls the GFCI is in the same box as the switch for the office lights. Maybe a short in the gang box?
 
15 amp Eaton breaker controls office and 3 hallway lights. 9 year old house. 200 amp panel.. Wind storm last week, breaker tripped. Re set it on, but it keeps tripping. Figured it was toast, so ordered a couple new breakers. (None in stock locally). Pulled an identical breaker from the panel and wired it in. It also tripped off, with a little spark. Any thoughts?
I know it’s been a long time since you posted this question but if you chang breakers and it still Tripp’s then you have a dead short somewhere
 

Reply to Circuit breaker keeps tripping in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

Hi all. We have a 120v 20 amp circuit to an accessory dwelling with a run of about 75' of direct bury #12. The breaker keeps tripping even when...
Replies
3
Views
288
I’m running wires to the basement for future basement finishing. I’d like to add two circuits of outlets (one on the finished side and one on the...
Replies
0
Views
591
Background Two weeks ago, lightning struck a tree in our yard. Many circuits tripped and several electronic devices failed. There was a strong...
Replies
2
Views
866
Hi All, I have a 1950s rental house with a 100 amp main panel with a main shut off breaker. Breakers are Eaton/Cutler Hammer type, so the...
Replies
2
Views
973
Summary (TL;DR) Several lightbulbs in my home supplied by one circuit breaker dim over time and go out in about a year. Right now, the ceiling...
Replies
0
Views
729

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock