Discuss Circuit Length in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Mark.W

-
Reaction score
31
Hi Peeps

I have my 2391 coming up in October and I am busy revising.

When determing the circuit length and VD, my notes say to link L - N at the load side and take the loop resistance at the DB.

The example I have is : Loop Resistance = 0.7 ohms (R) and csa of cable = 1mm2 (S), calculate the circuit length??

The formula they give is Circuit Length = 29.4 * R * S.

My question is where does the 29.4 come from??

Cheers
Mark
 
I always calculated circuit length by the R1 + R2 using the resistance of the cable given in the OSG guide Table 1A

So, if you divide the result of the R1+R2 test by this value it will give you the length of the cable. So say you have 2.5mm T+E with a 1.5mm CPC then that is 19.51.

You take your R1 + R2 reading and get say 0.54

0.54 ÷ (19.51 ÷ 1000) = 28.42 meters.

Is that 29.4 just a token resistivity example
 
Hi mate

The example they give is Circuit Length = 29.4 * R * S
The answer they give is Circuit Length = 29.4 * 0.7 * 1 = 20.6 metres
In other words they're muliplying the Loop Resistance of 0.7 by the csa of the cable 1mm2 by 29.4!!

I have never come accross this equation before? Confused.com
 
I think the 29.4 is made up. It's supposed to be the resistance in millohms per meter of the cable.
According to Table A.1 in GN3, it should be 36.2 when measured with an ambient temperature of 20ºC.
 
I think that's just a, poor, example.

Formula should be VD = ((mV/A/m) x L x Ib)/1000)

Where L is in meters and Ib is in Amps with the coefficients taken from appendix 4 of BS7671.
 
I think that's just a, poor, example.

Formula should be VD = ((mV/A/m) x L x Ib)/1000)

Where L is in meters and Ib is in Amps with the coefficients taken from appendix 4 of BS7671.
Aren't those values in Appendix 4, for when the conductors are at operating temperature?
 
Last edited by a moderator:
Hi Peeps

I have my 2391 coming up in October and I am busy revising.

When determing the circuit length and VD, my notes say to link L - N at the load side and take the loop resistance at the DB.

The example I have is : Loop Resistance = 0.7 ohms (R) and csa of cable = 1mm2 (S), calculate the circuit length??

The formula they give is Circuit Length = 29.4 * R * S.

My question is where does the 29.4 come from??

Cheers
Mark

If you've measured the l/n resistance, why do you need to work out the circuit length?

V=IR so you have R you just need the design current.

So with a L/N loop of .7 as per your example, if the design current was say 6 amps the volt drop would be .7X6 =4.2 volts. Job done.
 
Last edited:
If you've measured the l/n resistance, why do you need to work out the circuit length?

V=IR so you have R you just need the design current.

So with a L/N loop of .7 as per your example, if the design current was say 6 amps the volt drop would be .7X6 =4.2 volts. Job done.

That would actually be 0.7 x 6 x 1.2 = 5V as the resistance was measured at 20°C and volt drop needs to be corrected for the cable operating temperature of 70°C.
 
That would actually be 0.7 x 6 x 1.2 = 5V as the resistance was measured at 20°C and volt drop needs to be corrected for the cable operating temperature of 70°C.

You're right Jud, I'm just making the point that if the cable is already installed you are just verifying the volt drop, you only need to calculate the vd when you are designing a circuit.
Or is this something required for the 2391 exam? I must admit I never came across it.
 
Maybe just to show that you know how to work out the length of a circuit from resistance.

I must admit I've never done it using the formula in the OP. I do it the same way as malcolm said in post #2.

So it would be...

L = R ÷ (mΩ/m ÷ 1000)
L = 0.7 ÷ (36.2 ÷ 1000)
L = 0.7 ÷ 0.0362
L = 19.33m


L = length of circuit, R = measured resistance, mΩ/m = resistance per meter of 2 x 1mm² copper conductors (from Table 9A OSG or Table A.1 GN3)
 
Last edited by a moderator:
I take the measured value of resistance (0.7Ω), divide it by the value given in Table A.1 in GN3 or Table 9A in the OSG (36.2mΩ), and then multiply it by 1000, to change mΩ to Ω.
0.7 ÷ 36.2 = 0.01933 x 1000 = 19.33.
 
or you could just use a tape measure. only thing is i don't know how to correct the tape for expansion when warm.
 
I have been trying to work this out and, as in the case of others, have not seen this equation before. However the calculation does work out but the number 29.4 should be 27.6 by my calculations.

The proportional constant (in this case given as 29.4)

For Length L, resistance R and resistance per meter Rm
L = R / Rm
Or L = R * 1/Rm

When measuring at the db with L and N connected at the load you are measuring the resistance of twice the length of the circuit; once for the line conductor and then back for the neutral conductor.

So L = (R/2) * 1/Rm
This can be rearranged to give
L= R* 1/(2*Rm)


Given the resistance per meter of 1mm2 copper at 18.1mohm/m= 0.0181ohm/m
(From OSG table 9A appx 9 for a single 1mm2 cable (not the R1+R2 value)

1/(2*Rm) = 1/ 2*0.0181 = 27.6

So for a 1mm2 cable the length = R * 27.6

The length of the cable for any given resistance will be proportional to the csa.
I.e if the resistance R for a 1mm2 copper conductor gives a cable length of 1000m
Given the same resistance R but for a 2.5mm2 copper conductor the length must be increased by 2.5 i.e. 2500m

Therefore for any size cable the length L in relation to the resistance measured R and the csa S is as follows.

L = R * S * 27.6

Unfortunately this does not answer the original question where did 29.4 come from!
But at least it is closer
 
Yes, I got 27.6 as well.
It would be nice if there were a table of values, that you could then using a simple calculation X multiplied by the measured resistance = the length.
I generally end up doing the calculation two, three or how ever many times, just to confirm my results.
It doesn't help if you hit the + key on the calculator when you should have hit the x key, or you miss off one of the zeros when dividing by 1000.
Then there's those bloody scientific calculators!
 

Reply to Circuit Length in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Firstly, please go easy as I'm still a trainee! Working on my L3 2365 I'm having trouble understanding the rationale behind adiabatics...
Replies
3
Views
823
hi in college and watched some YouTube videos and read up on things I think I got the right formula but I'm not sure. Zsc= Zesc(or Zdbsc) +...
Replies
6
Views
2K
Hi there, I'm Currently doing my design calcs for my college project and doing the actual Zs calculation. Formula is Zs= Ze (or Zdb) + (R1+R2)...
Replies
1
Views
1K
Hello, I am a trainee electrician just starting to get into doing cable calculations. I understand them when it comes to a radial circuit but get...
Replies
5
Views
3K
Two related questions in 1, if anyone is up for helping! (i) When electricians install supplies, is there anything in the regs that says how many...
Replies
2
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock